In a message dated 97-04-03 22:42:10 EST, you write:

<< Subj:	plywood shear transfer detail
 Date:	97-04-03 22:42:10 EST
 From:	HARRISENGR(--nospam--at)aol.com
 Reply-to:	seaoc(--nospam--at)seaoc.org
 To:	seaoc(--nospam--at)seaoc.org
 
       I am refering to residential wood frame construction, with plywood
 shear panels.
       Typically, on the plans, i see a top plate shear transfer detail that
 shows a plywood panel edge nailed to the upper plate ( wood 2 x 4 ) of the
 double top plate then a simpson a35 to a block above.
      While performing structural observation today i see a problem that must
 be common:    The plywood panel is 8'tall-1/8". The wood wall is 8'-1" (
 92-1/4" studs ). With a minimum  !/2" ( even 3/8 " ) the top edge nails are
 either in the crack between the two top plates or in the bottom top plate
 that may ( probably ) not have appropriate shear transfer to the upper top
 plate and the a-35 above.  
      If the nails are angled, they must be over/under penetrating the plies
 by the nailhead.
 
      Since this is such a common condition , i would appreciate any thoughts
 on this detail.
      This may be hard to understand in this text but next time you observe
 the top plate edge nailing of an 8' shear panel you may see what i mean.
 
      Tom Harris, SE
      Thousand Oaks, CA
  >>

Tom,

This is a good reason for the need of structural observation of building
construction by the engineer of record.  Since the standard stud wall height
is 8'-1" or 97" tall (sill plate, stud, double top plate) and the plywood
sheet is only 95-7/8" tall this leaves a difference of  1-1/8".  The framer
needs to make sure they lift the plywood panel off of the floor about 1/2"
before they nail the sheathing to the wall. Using 1/2" edge distance for the
plywood nailing, you should still have about 3/8" to  1/2" to the bottom of
the top plate of the double top plate.  The same edge distances would also
apply at the sill plate.  Of course if you do not lift the plywood up, you
will be nailing in to the crack between the two plates if you use a 1/2" edge
distance.   After reading your post,  I will probably add a note about this
to our general notes regarding holding up the plywood sheathing.

I know that tradtionally for many years the clear height from floor to
finished ceiling is suppose to be 8'-0" (97"stud wall height minus 1" for
finish ceiling), but I am cursious to know why the 8'-0" clear height was
selected orignially as opposed to say a 10'-0" ceiling height which you often
might see in a custom home.  Was this originally because of costs or
manufactoring restrictions? 

Curious

Michael Cochran


--- Internet Message Header Follows ---
Received: from server1.seaoc.org (bqe.com [204.140.166.34])
	by host1.texramp.net (8.8.5/8.8.5) with SMTP id WAA03486
	for <rlewis(--nospam--at)techteam.org>; Fri, 4 Apr 1997 22:20:16 -0600 (CST)
Received: from emout19.mx.aol.com by server1.seaoc.org (NTList 3.02.10) id
ka016546; Fri, 4 Apr 1997 20:07:25 -0800
Received: (from root@localhost)
	  by emout19.mail.aol.com (8.7.6/8.7.3/AOL-2.0.0)
	  id XAA20113 for seaoc(--nospam--at)seaoc.org;
	  Fri, 4 Apr 1997 23:05:02 -0500 (EST)
Date: Fri, 4 Apr 1997 23:05:02 -0500 (EST)
From: BCASE1356(--nospam--at)aol.com
Message-ID: <970404230451_607358273(--nospam--at)emout19.mail.aol.com>
To: seaoc(--nospam--at)seaoc.org
Subject: Re: plywood shear transfer detail
Reply-To: seaoc(--nospam--at)seaoc.org
Error-To: seaoc-ad(--nospam--at)seaoc.org
X-Loop: seaoc(--nospam--at)seaoc.org
X-Info: [SEAOC]
Owner: seaoc-ad(--nospam--at)seaoc.org
X-POP3-Rcpt: seaoc-ad(--nospam--at)seaoc.org
X-Sender: seaoc-ad(--nospam--at)seaoc.org
Precedence: list
X-ListMember: rlewis(--nospam--at)techteam.org [seaoc(--nospam--at)seaoc.org]


__________________________________________________

Richard Lewis, P.E.
Missionary TECH Team
rlewis(--nospam--at)techteam.org

The service mission like-minded Christian organizations
may turn to for technical assistance and know-how.