  Karen,

  I wonder what the failure mode was in the test reports you mention.  Was
it the anchorage or the joints between the blocks.  I have had some
experience constructing glass block panels and it seems to me if the panel
were very large they would fail at the joints in the middle if a
distributed load were applied.

  Good luck

  Daniel Del Carlo

On Sat, 10 Jan 1998, kcasano wrote:

> I'm looking for some input on the anchoring of glass block wall panels. 
> I am working with a group of architects who feel that using steel
> channels along the top and sides of the wall panel will detract too much
> from the architectural statement of the building.  UBC section 2110
> clearly allows the use of "panel anchors" to anchor glass block, but
> also requires that the panels be anchored for a minimum load of 200
> lbs/ft.  I am having trouble quantifying the allowable load for these
> anchors (as well as satisfying myself that a light gage metal strap
> perpendicular to the direction of the load can provide a positive
> connection).
> 
> I have spoken with members of ICBO, the International Masonry
> Association, The Masonry Association of California, and Pittsburg
> Corning in regard to this issue and still have nothing definitive.  The
> best and most relevant information I received from Pittsburg Corning was
> a copy of some testing which was performed on some 12 ft square glass
> block panels anchored to a frame with panel anchors at 16 inches on
> center on both sides and across the top.  The panel was loaded with a
> constant pressure by inflating air bags on the face.  Failure of the
> panel anchors was recorded at a pressure of 60 lbs/sq ft.  It has been
> my experience that a safety factor of 4 is ordinarily used on ultimate
> failure loads such as this. That would leave me with an allowable design
> load of 15 lbs/ sq ft which may meet wind and seismic criteria, but will
> not meet the requirement for anchorage in the code -  even if I double
> the anchors to 8 inches on center.  Am I applying too great a safetly
> factor? 
> 
> Any comments or advice? 
> 
> Karen E. Casano, CE
> Biggs Cardosa Associates
> San Jose, Ca.
> 
> 
> 
>