How do you achieve top (3/4") and bottom (3") clearance of the
reinforcing with a 4" slab?  I've always gone to a 5" slab when using
reinforcing.  Often times the client is not willing to pay for this and
I've been pushed back to using a 4" slab with wwf (even though we know
clearance was not maintained here either!).
Bob Germaine PE

> ----------
> From: 	Smikeng[SMTP:Smikeng(--nospam--at)aol.com]
> Sent: 	Monday, April 20, 1998 9:04 PM
> To: 	seaoc(--nospam--at)seaoc.org
> Subject: 	Re: SLAB - Control Joints in Concrete Slab on Grade
> 
> We spec fibermesh for 2" topping slabs with good results, however, we
> always
> spec #4 @ 24 " o.c.  or #3 @ 18" o.c. for slabs on grade (Provided
> more
> stringent requirements are not reccommended by the soils engineer).
> Although
> #3 are our preference for 4" slabs, we have actually seen concrete
> installers
> remove the spacers because the 18" spacing is too tight and causes
> them to
> trip!!
> 
> 
>