On 5/12, Martha Alic wrote:

> I have designed a one story steel-framed mezzanine with braced frames in one
> direction and monent frames on the other direction. These moment frames are
> not part of the primary building frame system. The moment frame member design
> is governed by seismic load and the Rw used was for OMRF, but the final member
> sizes are based on drift limitations (since a pinned base was used the drift
> is high, even under low seismic forces). 
> 
> Considering FEMA 267 moment connection design guidelines, the criteria apply
> to all SMRF structures designed for eathquake and OMRF structures located
> in...seismic zones 3 and 4. Light single story buildings, the design of which
> is governed by wind need not consider this interim guidelines. 
> 
> Do the moment connections need to comply with FEMA guidelines or can the
> connection be designed for 3Rw/8*the prescribed lateral forces. Is there
> another alternative to design this connection?
> thanks
> 
Recent testing by Subash Goel at the Univ. of Michigan Ann Arbor 
demonstrates that even connections employing light framing members, 
but using typical pre-Northridge detailing are vulnerable to 
premature fracture - at very low plastic rotation demands.  The 
connections should be designed per SAC FEMA-267 recommendations, 
unless they can remain elastic.  3/8Rw loads does not guarantee 
elastic response.  The real loads for elastic response are something 
like Rw/1.4/1.5 times the code specified forces.  The 1.4 is the 
inherent load factor on Rw.  The 1.5 is an estimate of material 
overstrength.Ronald O. Hamburger, SE
Regional Manager
EQE International, Inc.