Of course you cannot use a "typical" anchor bolt (based on UBC table 19-E)
for hold downs. You have to use something more substantial, but not unusual,
such as a Simpson STAB bolt or some other anchor. If the world of tension
anchors were limited to UBC table 19-E, we all would be in a bind.

Regards,
Bill Allen

-----Original Message-----
From: Truong Huynh [mailto:THUYNH(--nospam--at)BAS.CI.LA.CA.US]
Sent: Friday, September 04, 1998 11:40 AM
To: seaint(--nospam--at)seaint.org
Subject: Re: 3/8 inch shear panels -Reply


For shear wall with uplift forces around 5 to 6 kips may not be a problem
for
the holdown device.  The problem, however, are usually with the holdown
anchor
bolts and required edge distance.

Allowable service load (building code table 19-e) for a typical 5/8" dia
anchor
bolt embedded in f'c of 2500psi with 3-3/4 edge distance is 1500 lbs.  The
shearwall and holdown device may not fail, but the anchorage certainly will.

City of LA
Building Dept.