Thanks for the offer. My FAX number is 619-556-0639. Where should I
look for the information which specifically allows seismic loading? I have
been curious about this issue for quite some time. Thanks to for
mentioning your original post on the SEAINT listserver.

>>> "Anderson Pete (ap)" <ANDEPET(--nospam--at)us.hilti.com> 09/22/98 04:16am
>>>
Both reports were renewed as of July 1, 1998 and specifically allow for
seismic laoding.  Call me direct at 1-800-879-6000 X6884 and I will fax
them to you.  Or you can E-mail me your fax number and I will send them.


Pete Anderson
Hilti, Inc.  

> ----------
> From: 	John Armijo[SMTP:421jarmi(--nospam--at)pwcsd.nosc.mil]
> Sent: 	Monday, September 21, 1998 5:23 PM
> To: 	seaint(--nospam--at)seaint.org
> Cc: 	Anderson Pete (ap)
> Subject: 	RE: Epoxy Anchor -Reply
> 
> ER 4627 (Kwik-Bolt II) dated July 1, 1996 was FAXED to me today from
> 1-800-879-8000. ER 4627 has a sentence in the Findings section of the
> report that reads, "6. Use of the anchors in resisting wind and
> seismic
> forces is beyond the scope of this report."
> 
> The Findings section of ER 3987 dated July 1, 1996 does not have the
> wind and seismic disclaimer above. But, it also does not specifically
> mention that it is usable for wind or seismic loads.
> 
> Did I get an old copy of the reports since the reports are subject to
> re-examination in two years from July 1, 1996? 
> 
> 
> >>> "Anderson Pete (ap)" <ANDEPET(--nospam--at)us.hilti.com> 09/21/98 08:58am
> >>>
> 
> Both the HSL and the KWIK BOLT II have been listed by ICBO ES for
> seismic loading.  See latest versions of ER #4627 and ER #3987.
> Contact
> Hilti at 1-800-879-8000 for current copies.  
>   	 
> 
> > ----------
> > From: 	Lynn[SMTP:lhoward(--nospam--at)silcom.com]
> > Reply To: 	seaint(--nospam--at)seaint.org
> > Sent: 	Thursday, September 17, 1998 7:32 PM
> > To: 	seaint(--nospam--at)seaint.org
> > Subject: 	Re: Epoxy Anchor
> > 
> > We have just been through a similar issue with OSHPD on a hospital
> > project.  Because epoxy anchors do indeed loose significant strength
> > when
> > heated, they should not be used to support any kind of gravity
> > loading.
> > If the anchors are just carrying seismic or wind loads, OSHPD (and I
> > assume DSA) will in fact allow the use of epoxy anchors.
> > 
> > The problem with expansion bolt is that with the exception of the
> > HILTI
> > HSL anchors, none of the expansion type anchors have ICBO
approved
> > design
> > values for seismic loads.  The HILTI HSL anchors are metric, made in
> > Germany, and are very expensive.
> > 
> > OSHPD will in fact accept the HILTI KWIK BOLT II for use as seismic
> > anchors if you use 80% of the ICBO number for gravity loads for
> shear
> > or
> > tension.  However, there could be a problem down the road when the
> new
> > ICBO reports come out if the allowable shear and tension values are
> > lower
> > than what OSHPD is currently allowing.  Admittedly the chance of
> this
> > happening is small.
> > 
> > In our case, we ended  up using epoxy anchors because all of our
> work
> > involved anchors that only carried seismic anchors for floor mounted
> > equipment.
> > 
> > Good Luck
> > 
> > Lynn
> > 
> > 
> > 
> > 
> > James Lin wrote:
> > 
> > Project: Retrofit the existing concrete building (school job)
> > 
> > > Location: Southern California
> > > DSA correction: Use drilled and grout anchor bolts (instead of
> Hilti
> > > Hit HY150) to fasten new steel ledgers to existing concrete walls
> > > (Since raised temperature during fire will reduce the bond
> strength
> > of
> > > epoxy anchors)
> > >
> > > We still like to use epoxy anchors for the following reasons
> > > 1. better quality control (for installation) over drilled and
> grout
> > > anchors
> > > 2. less chance to cut the existing rebars
> > >
> > > Any opinion/suggestion to response to DSA (Department of State
> > > Architect of California)?
> > >
> > > Thanks in advance
> > >
> > > James Lin, S.E.
> > > I. D. S.
> > >
> > >
> > 
> > 
> > 
> > 
> 
> 
>