Proof testing a soil or rock anchor to 1/3 of its design load proves it can
withstand [or not withstand] 1/3 of its design load.

Typically performance and proof tests (not the same thing) test an anchor to
1.33xDesign Load, although occasionally 1.5x is specified.

For a much more definitive discussion refer to:

"Recommendations For Prestressed Rock and Soil Anchors"
POST-TENSIONING INSTITUTE
171 W. Northern Ave, Suite 218
Phoenix, AZ 85021
(602)870-7540
The 1986 edition was $9.00

3.0 ROCK ANCHORS
Section 3.7 Anchor Testing and Stressing
Section 3.7.1 Performance Test
Section 3.7.2 Proof Test
Section 3.7.3 Creep Test
Section 3.7.4 Further Checks

5.0 SOIL ANCHORS
Section 5.5 Anchor Testing and Stressing
Section 5.5.1 Performance Test
Section 5.5.2 Proof Test
Section 5.5.3 Creep Test
Section 5.5.4 Further Checks

You also could contact the nearest office of Dywidag Systems International
for technical assistance. I'm not sure who they have in the pacific
northwest. Their western division headquarters is in Long Beach, CA
(562)531-6161. Ask for Mike Kelley.

Hope this helps,

Brent Koch
Livermore, CA
Brent(--nospam--at)willislivermore.com



-----Original Message-----
From: Freilinger, Shawn W [mailto:Shawn(--nospam--at)Valmont.com]
Sent: Monday, October 12, 1998 3:18 PM
To: 'SEAINT Mailing List'
Subject: ROCK ANCHOR PROOF TESTING


		I am design a rock anchor foundation for a
telecommunications tower.  Is anyone familiar with proof testing of these
rods?  The anchors are about 11' deep into solid bedrock.

		My company has required a couple different ways of proof
testing these in the past.  One method is to grout the bottom 1/3 of the
hole and then pull with a third of the expected anchor tension.  The other
method is to grout the entire bar and then proof test it for combined
stresses (bending and tension).

		If anyone has some "standard practice" knowledge or reading
resources, I would appreciate it.

		Thanks,
		Shawn

		Shawn Wicks Freilinger
		Valmont/Microflect
		Shawn(--nospam--at)valmont.com <mailto:Shawn(--nospam--at)valmont.com>