Sib - 

A couple of more things to consider (for future reference).  If you do place
the baseplates on levelling nuts, remember that the anchor bolts will be
subjected to bending stresses in the event that the baseplate connection is
asked to transfer shear.  Additionally, a check should be made for prying
forces unless the baseplate is flexurally stiff relative to the axial
stiffness of the anchor bolts.

Regards,

J. Silva, SE
Hilti, Inc. 
silva(--nospam--at)hilti.com

> ----------
> From: 	Sibco6756(--nospam--at)aol.com[SMTP:Sibco6756(--nospam--at)aol.com]
> Reply To: 	seaint(--nospam--at)seaint.org
> Sent: 	Thursday, February 11, 1999 11:07 AM
> To: 	seaint(--nospam--at)seaint.org
> Subject: 	baseplate analysis problem
> 
> 
> I have a problem where I must now check several baseplates that have
> misplaced
> (off center) columns.  The columns have axial load and moments with anchor
> bolts at the corners.  Checking by the hand methods has shown overstress
> in
> bolts and the plate so I must need to do a more detailed check. ( The
> framing
> has been built, so replacing or moving the baseplate will be difficult, I
> can,
> however, drill in more anchor bolts )
> 
> The current software program I use for baseplate design will not do this
> analysis - does anyone have suggestions on other methods or softwares that
> can
> be used to solve problems of this type ? 
> 
> many thanks for any help that can be provided,
> 
> -sib
> 
> 
>