RE: Required wall attachment to a flexible diaphragm.

[Subject Prev][Subject Next][Thread Prev][Thread Next]
If you are talking about anchorage to a flexible diaphragm of tilt-up of
masonry wall, then ap = 1.5 otherwise 1.0.
Rp is 3.0 unless you do not meet the shallow anchorage requirement which
is the anchor in the wall must be embedded 8 times its diameter (i.e.
3/4" A.B. must have 6" embedment) otherwise your Rp equals 1.5 and your
force doubles.

The force (Fp) applies to Anchor bolts, prefabricated HD's & CT's etc..,
and all elements of the wall anchorage system (Struts, cross-ties,
chords, and subdiaphragms.) Note that Steel elements must be designed to
resist 1.4 times the force generated by the Fp equation (In ASD & LRFD
steel design). That means anchor bolts, metal straps (steel only, not
nails in wood- [that's the way I read it]), and simpson/kc metals/zone 4
hardware must be selected to meet this increased force. But the wood
elements, i.e. struts, bolted and nailed connections, and subdiaphragms
need only be designed to resist 0.85Fp. Soil type D yields the worst
results.

Yes . . . the forces get very high . . . don't use shallow anchors!!! 

Confusing Ain't it. We'll get used to it. (hopefully)

Gerard Madden, P.E.
Civil Engineer, Associate
CRJ Associates, Inc.
email: gerardm(--nospam--at)crjarch.com
tel: 650.324.0691
fax: 650.324.0927
web: www.crjarch.com



> -----Original Message-----
> From:	From the desk of Joe Otto [SMTP:jmo_engineering(--nospam--at)email.msn.com]
> Sent:	Thursday, August 26, 1999 2:36 PM
> To:	Seaint@Seaint. Org
> Subject:	Required wall attachment to a flexible diaphragm.
> 
> The 1997 UBC Section 1633.2.8.1.1 indicates the values for Rp and Ap
> of 3.0
> and 1.5 respectively should be used for elements of the wall anchorage
> system.
> 
> What are the components of the wall anchorage system that these values
> apply
> to?  Is it the attachment of the wall to the diaphragm.  Or does this
> also
> include the subdiaphragms and cross-ties?
> 
> if hx = hr ==> Fp = ap*Ca*Ip/Rp*(4Wp)
> 			= 1.5 * (.44*1.2) * 1.0 / 3 * 4 * Wp  = 1.06Wp
> 
> This seems high to me.  If anyone could take the time to
> clarify/confirm
> this, it would be appreciated.
> 
> Thanks in advance.
> 
> Joseph M. Otto, PE
> Ireland Engineering
> Fremont, CA
> 
> 
> 
>