1997 UBC Section 1632.2 clearly defines h-sub-x as the element or component
attachment elevation with respect to grade.  The key words are attachment
elevations.  These are discrete points, each with a unique value.  F-sub-p
values should not be determined at elevations that do not involve attachments to
the structure, such as the middle of a panel.  1997 UBC Section 1632.2  goes on
to specify that design lateral forces shall be distributed in proportion to the
mass distribution of the element or component.

So how do we apply these requirements to panels attached at different
elevations?  The UBC is silent, allowing for engineering interpretation.  (No
matter how conscientious, code writers just can't anticipate each and every
situation.)  However, SEAOC made certain that panels were addressed in their
Design Manual Volume 1.   The example uses an average panel design value of the
F-sub-p values for each attachment elevation.  This is one rational engineering
interpretation for this application, and one that is relatively easy to use.
Another rational engineering interpretation would be to apply a straight line
(trapezoidal) distribution between the F-sub-P values.  This causes a little
more work for the engineer, and therefore, was not suggested in the Design
Manual.  I suggest that we all follow the SEAOC Design Manual Volume 1.

So how do we apply these requirements to block walls/fences?  Block walls have
one attachment point, at grade.  F-sub-p values should be determined at grade
level only.  There is no need to complicate the problem and determine F-sub-p
values at the top of the wall where there are no attachments.

Hope this helps.

Rick Drake, SE
Fluor Daniel, Inc.
Aliso Viejo, CA

                                                                
 -------------------------------------------------------------- 
 The information transmitted is intended only for the person or 
 entity to which it is addressed and may contain confidential   
 and/or privileged material. If you are not the intended        
 recipient of this message you are hereby notified that any     
 use, review, retransmission, dissemination, distribution,      
 reproduction or any action taken in reliance upon this message 
 is prohibited. If you received this in error, please contact   
 the sender and delete the material from any computer.  Any     
 views expressed in this message are those of the individual    
 sender and may not necessarily reflect the views of the        
 company.                                                       
 --------------------------------------------------------------