Can anyone lead me to a source to prove that a hooked anchor bolt (j-bolt)
can develop the loads typically used for hold downs when cast into a stem
wall.

Using section 1925.3.2 ('94 UBC) with a phi factor of .85 (assuming the
j-bolt is hooks around a horizontal bar) and an edge distance of 2.75 inches
(assuming an 8 inch stem wall but the bolt is centered in a 5-1/2 inch 2x6
plate), what should the value be for As?

If I use concervatively a truncated cone with a diameter of 5.5 inches and
an embedment length of 2.75" so as not to have to reduce for lack of edge
distance, I come up with a tension value of 4045# for 2500 psi concrete.
For service load design, this would need to be reduced by a load factor of
1.3 for wind and 2.0 for no special inspection which results in a value of
1555#.  This does not develop the load for even an HD2A bolted to a double
stud.

I assume it is acceptable to use more surface area then this conservative
assumption but the question is how much and how is it justified?

Thanks in advance for any input.