Use option (a).

I would be inclined to use a welded splice.  A coupler is better regarding
strength, but they are bigger than the parent bar and will increase the
requirement for cover.  I would chip out enough concrete to stagger the
splice location.  If you have a mill cert, preheat according to the CE.  If
you don't, you will need to assume worst case CE and preheat accordingly.

Depending on the CE, I would be more inclined to use a welded lap splice as
opposed to a welded butt splice.  If the CE is low, and the welder and
inspectors are good, a butt splice can be used.

Use an ASTM A706 splice bar.

Use certified welders, and require special inspection!!!

Regards,
Harold Sprague


> -----Original Message-----
> From:	Tony Diaz [SMTP:ad(--nospam--at)freese.com]
> Sent:	Tuesday, June 27, 2000 8:55 AM
> To:	seaint(--nospam--at)seaint.org
> Subject:	cored concrete beams
> 
> I have a "situation" and am soliciting help from all of you helpful 
> folks.  Several existing reinforced concrete beams were cored by 
> electricians who mistook a deep concrete beam for a CMU wall. 
> Unfortunately, all six of the cores were taken near the bottom of the 
> beam at midspan. Three #10 bars were cored completely thru.
> 
> My proposed repair would be to either:
> 
> 	a) expose enough rebar to splice with Bar-Splicer or welded 	
> 	splice, then use repair material to patch or
> 
> 	b) use an external steel plate on each side of the beam using  
> 	thru bolts as needed to carry the stress.
> 
> This happened at several beams with different rebars cut but 
> essentially the same results. The beams are either 16 or 28 inches 
> wide and 41 inches deep. Currently, the existing beams are 
> probably being partially supported by an existing CMU wall 
> underneath it. Any suggestions would be appreciated. Thanks.
> 