Dave,

There was a guideline that was developed for Butler Manufacturing called
"Foundation Design and Construction Manual".  It was developed by the people
at Computerized Structural Design, Inc. They developed a methodology that
given a thrust magnitude calculates the length of hairpin required for a
given mesh.  You have to transfer the forces from the hairpins into the
mesh.  The mesh then either uses the slab in friction to resist the thrust
or ties the 3 hinged arch together.

The UBC 1907.12 values are for slab shrinkage only, and have nothing to do
with the applied lateral thrust.

There is no real code guidance here.  You will just have to use first
principles.  You will have to develop the reinforcing required based on
acceptable performance (crack acceptability), and calculate the flexural
reinforcing, the temperature / shrinkage reinforcing, and the reinforcing
required to develop the thrust in the hairpins.

Engineering unencumbered by the whims of code moguls.

Regards,
Harold Sprague


> -----Original Message-----
> From:	Dave Adams [SMTP:davea(--nospam--at)laneengineers.com]
> Sent:	Friday, September 29, 2000 5:55 PM
> To:	seaint(--nospam--at)seaint.org
> Subject:	Reinforcing for a Metal Building System Slab-on-Grade
> 
> Hello all,
> 
> I apologize if this is a discussion that has been brought up before. 
> 
> What minimum amount of reinforcing meets Code requirements when hairpins
> are
> present in a slab-on-grade with, perhaps, fork lift traffic but no heavy
> storage rack leg loads? It seems that it would be appropriate to at least
> provide enough steel required to transfer the hairpin forces and tie
> everything together (possible unequal distribution of support for forklift
> loads, etc.), but is there a need to consider the minimums per Section
> 1907.12 as applicable?
> 
> This may be one of those "bonehead" questions, but I'd like to know what
> the
> consensus is (if there is one).
> 
> 
> TIA,
> Dave K. Adams, S.E.
> Lane Engineers, Inc.
>