1997 UBC Equation 12-16-1 is posted by ICBO as an errata.  It reads 0.9D
plus or minus E/1.4.

Rick Drake, SE
Fluor Daniel, Aliso Viejo

*****************************





James_F_Fulton(--nospam--at)RohmHaas.Com (James F Fulton) on 11/15/2000 06:13:48 AM

Please respond to seaint(--nospam--at)seaint.org

To:   seaint(--nospam--at)seaint.org
cc:

Subject:  ASD Load Combinations


Based on commentary in ASCE 7-95, the 1/3 allowable stress increase on
combined stress, or its equivalent the 0.75 load factor, is allowed only
when
two or more "transient" loads are contained within the load combination.
[This of course is counter to long past practice, as reflected for one in
the
AISC Spec (see ASD 9th, A5.2) , but it appears to be the re-think today].
Equations (12-7) through (12-11) are consistent with this new thinking,
except it appears for (12-8) since there is a low probabiliity that L and
Lr
or S would occur at the same time (but not as low of a probability of L and
W
or E occuring at the same time -- say OK).

Equations (12-12) through (12-16) are also consistent with the new criteria
if one interprets the INTENT of the equations as written this way: In
(12-13)
for example, D + L + (W + E/1.4), the L cannot be taken as zero such that D
+
(W +E/1.4) results to which a 1/3 stress increase is applied. In other
words,
in all the equations for the 1/3 increase to apply, ALL individual loads
must
be included, and none excluded. This is the interpretation I have to make
for
this to be consistent and make sense. However,  suppose you do not have a
"L", which can occur for non-building structures such as vessels/ tanks, or
"L" happens to be very small for some reason. Looks like there is no load
combination in the (12-12) through (12-16) group that covers this situation
because there is no D + (W or E/1.4) combination similar to (12-9). So, you
are stuck with (12-13) which becomes in effect D + (W or E/1.4) to which
allowable stresses are increased by 1/3. To me this appears to be
inconsistent and an oversight.









-----------------------------------------------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain confidential
and/or privileged material. If you are not the intended recipient 
of this message you are hereby notified that any use, review,
retransmission, dissemination, distribution, reproduction or any
action taken in reliance upon this message is prohibited. If you 
received this in error, please contact the sender and delete the 
material from any computer.  Any views expressed in this message
are those of the individual sender and may not necessarily reflect 
the views of the company.  
-------------------------------------------------------------------------------------------------------