Jason Emoto wrote:

>>UBC Sections 2106.1.12.3 and 2106.1.12.4 specify minimum reinforcing ratios
depending upon seismic zone.  In seismic zones 3 and 4, maximum reinforcing
spacing is 4 feet (2106.1.12.4.2.2.3).<<

But beware of the UBC reinforcing requirements for Seismic Zone 2!  These 
reinforcing requirements are the result of HUD tests for *small* (< 2500 sf), 
lightly loaded, single story, one- or two-family residences and were somehow 
extrapolated to be permitted for buildings of *any* occupancy, height, and 
loading conditions in Seismic Zone 2.

>>Bond beams are not specifically required, though. You can use joint 
reinforcing to satisfy minimum reinforcing requirements.<<

If you carefully read brochures for joint reinforcing such as produced by 
Dur-O-Wal and AA, I think that you will find that joint reinforcing is 
restricted to crack control usage, and is not authorized to resist stress.