>I still think it would hurt if a pallet full of TV's was launched off the
>top shelf of a 16 foot tall storage rack onto my head.
It can get a little dicier than that. I got involved in a document 
storage warehouse where the racks collapsed progressively over 20-30 
minutes after someone ran a forklift into one leg of one rack. One rack 
tips into its neighbor, boxes start sliding, the bottom couple of layers 
buckle backwards and hits the rack on the other side. Boxes slide and 
fall more racks start tipping into each other, and every single 15-20 
foot high rack in the area went down. This was in Minnesota with no 
seismic requirements, so no requirements to tie the tops to each other or 
anything else. Simple good sense dictates doing so, but you know the 
if-the-code-doesn't-make-us-use-our-brains-the-hell-with-it approach. For 
a while afterwards, there was still some question about whether anyone 
was buried in it all. Took a while to get down to the forklift that 
started it all.

You never saw such a mess. The floor was 8-10 feet deep in boxes of 
documents strewn in and around the ruins of the shelving. Climbing around 
the stuff during the investigation was almost surreal. By luck none of 
the supporting columns was damaged so the roof stayed put. The crew that 
was working there didn't have wit enough to get out quick--fascinated by 
the domino stack going down I guess.

Christopher Wright P.E.    |"They couldn't hit an elephant from
chrisw(--nospam--at)skypoint.com        | this distance"   (last words of Gen.
___________________________| John Sedgwick, Spotsylvania 1864)