The IBC requires each end of each full height piece to be restrained even
when using a perforated methodology.  The last draft of the 2000 NEHRP I saw
has the following provisions:



for full height segment bottom plate - top plate shear connection:

vdesign=V/[Co*sum(Li)] 



for full height segment bottom plate uplift connection:

tdesign=V/[Co*sum(Li)] 



for shearwall chord tension at the extreme ends of the wall

Tdesign=vdesign*H


for wall nailing:

vtable*Co < V/sum(Li)


The NEHRP also limits the wall shear strength to 640 plf, says to design
collectors, limits wall height, requires anchors to have direct load path to
foundation and does not mention using gravity loads to resist
overturning-uplift.

Scott M Haan  P.E.
Plan Review Engineer
Building Safety Division http://www.muni.org/building, 
Development Services Department,
Municipality of Anchorage
phone: 907-343-8183   fax: 907-249-7399
mailto:haansm(--nospam--at)ci.anchorage.ak.us

> -----Original Message-----
> From:	David B Merrick [SMTP:mrkgp(--nospam--at)pacbell.net]
> Sent:	Friday, March 30, 2001 2:19 AM
> To:	seaint(--nospam--at)seaint.org
> Subject:	Re: Wood Shear Walls
> 
> recall my quest of last week and I concluded with the equation that
> represents
> the chart in the IBC2000
> 
> Co = 100/(B(1-3A)+3A)
> 
> Reference table 2305.3.7.2
> 
> Let A= the ratio of maximum opening height to the wall height.
> That's the value across the top of the chart.
> 
> Let B= percent of full height sheathing to full length of wall.
> That's the left column on chart.
> 
> 
> 
> Jason Kilgore wrote:
> 
> > Ok, the subject is back.
> >
> > I recently received a 3-story wood project.  It's a teen shelter shaped
> like
> > a house, 50'x60'.
> >
> > The problem is that the architect is apparently into the "swiss-cheese"
> > look.  I can't find a single patch of wall more than 3ft wide extending
> from
> > the foundation to the roof.
> > None of the windows and doors line up.  Walls move in and out of plane.
> >
> > Anyone know of a good reference for designing such a beast?
> >
> > The walls will have to be designed as big shear walls with holes.  Is
> there
> > a reference for nailing patterns around the openings?  Does the UBC
> contain
> > this information.
> >
> > Speaking of the UBC, the city where this is located is still using the
> 1991
> > UBC.
> >
> > ----
> > Jason W. Kilgore, P.E.
> > Leigh & O'Kane, L.L.C.
> > jkilgore(--nospam--at)leok.com
> > (816) 444-3144
> >
> 
> 
>