Brian Smith wrote:

. > You project down, from your bearing surface, at 45 degrees, either side of
. > the bearing plate, to a maximum width of 4*t + brg or the center to center
. > spacing of the point loads, whichever is smaller.


A number of years ago, there was a paper written on the distribution of a 
concentrated load thru a bond beam --- the intent, IIRC, was to determine how 
deep a concrete bond beam needed to be to distribute the concentrated load 
onto cmu below the bond beam and to test whether the 45 deg assumption was 
valid.  The finding was that the concentrated load distributed closer to 30 
deg. then it did to 45 deg.

A. Roger Turk, P.E.(Structural)
Tucson, Arizona