As a nominal tolerance, 1/16" plus/minus from 3/8" nominal panel edge nailing
distance is reasonable recommendation. In APA shear wall and diaphragm tests,
and in some tests by others (such as UC-Irvine), proper edge nailing distance is
assured by chalklines placed around panel edges during fabrication. Contact APA
Help Desk (www.help(--nospam--at)apawood.org) for official position on tolerance for panel
edge nailing distance, as well as for panel edge spacing and limits on
"overnailing" guidelines.
John Rose/APA (retired)

"George Richards, P.E." wrote:

> John:
>
> Most materials have plus-minus tolerances on installation. What would you
> say is the plus-minus tolerance on edge distances?  Many of us go out to the
> job site and would like some good guidance on this issue.  As a practical
> matter we recognize that holding a framer to a 1/16 inch tolerance which is
> one half the diameter of an 8d common is likely to cause the framer to turn
> is framing gun on us.
>
> Thanks, George Richards
>
> -----Original Message-----
> From: John Rose [mailto:jrose36(--nospam--at)earthlink.net]
> Sent: Wednesday, April 18, 2001 7:12 PM
> To: seaint(--nospam--at)seaint.org
> Subject: Re: Gaps between plywood sheathing
>
> Intended wood structural panel sheathing installation, measured from
> centerline of 2x framing:
> 1/16" panel edge gap (one-half of 1/8" spacing between panels)
> 3/8" panel edge nailing distance (minimum)
> 5/16" framing edge nailing distance
> Total = 3/4" or one-half of 1-1/2" thick framing member.
>
> In LA, shear wall requirements dictate 1/2" panel edge nailing distance,
> instead of 3/8" as above, when shear loads exceed 300 or 350 plf. In this
> case, the framing thickness must be increased to 3x where panel edges occur
> on the same framing member. At top and bottom plates of walls, there is
> adequate framing thickness at these locations to provide 3/4" panel edge
> nailing distance in most instances, so 2x framing usually is adequate,
> although the IBC and UBC may dictate 3x framing for these applications. The
> extra edge distance improves lateral nail resistance against "pull out"
> through panel edges, if nail forces are perpendicular or at an angle to the
> panel edges, as sometimes occurs near corners of sheathing panels.
>
> John Rose/APA (retired)
>
> Michael Bryson wrote:
>
> Typically you install sheathing with a 1/8" gap between sheets to allow for
> some expansion, correct? If the sheets are supported by a 2x framing member,
> how do you get your edge distance for a 10d nail?
>
>  <http://www.structuralist.net/AutoList.htm>
>
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org


* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org