Actually, some building codes DO specify drift limits for seismic loading.
I know that BOCA (93 and 96), IBC (2000), UBC (97), and SBC (91 is all I
have access to) have drift limitation for seismic loading.

I am NOT aware of any specified drift limitations in any codes for wind
loading.  I AM aware of some guidelines.  One of AISC's Design Guides (I
believe No. 3: Serviceability Design Consideration for Low-Rise Buildings)
does provide some suggestions/guidelines.

HTH,

Scott
Ypsilanti, MI


On Wed, 27 Jun 2001, Bill  Marczewski wrote:

> John:
>  
> As you probably know, few codes or standards address drift limitations.  I
> work in seismic zone 1 (Denver, Colorado), and we therefore limit our
> building drift to account for a desired building performance due to wind
> loading.  For wind drift on buildings we typically limit those values from
> 0.0015 to 0.0035 times the building/story height, and simultaneously limit
> seismic drift to a value of about 10 times greater (0.015 to 0.035).
>  
> As in the case of your auto dealership, I concur with the previous response
> from another, that the window manufacturer or architect can provide
> information on how much movement the window can tolerate within the frame.
> We often ask this question when designing office buildings to determine how
> much beam deflection to allow.  The typical response is that the window can
> move about 1/2" within the window frame.
>  
> If you have a higher risk of an seismic event than we do here in Denver,
> than I would suggest you consider designing your structure to account for
> drift due to seismic forces with (0.0035)*(H) being your maximum allowable
> displacement.  In doing so, you should have covered drift requirements for
> daily loadings such as wind/gusts, and still have a sound structure after a
> seismic event.
>  
> Bill S. Marczewski 
> Denver, CO 80210 
> bmarczewski(--nospam--at)martind.com <mailto:bmarczewski(--nospam--at)martind.com> 
> 
>  
> 
>  
> 


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********