What you are "missing" is a matter of naming convention; many people
use the same name for two very different things.

The perforated shear walls described in your APA reference are those
for which an empirical design approach is provided in the 2000 IBC and
the 2000 NEHRP Recommended Provisions (among other places).  [In the
IBC this is called "no force transfer around openings."]

The perforated shear walls that Gerard mentioned and for which the
extensive calculations are required are those with "force transfer
around openings" (to quote the IBC).  Where the design includes
explicit calculation of forces at openings (and provides suitable
strapping, etc.) the aspect ratio limits apply to the entire wall
(including openings) and to the wall piers measured from bottom to top
of opening (not bottom to top of wall).

-Mike

- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Michael Valley, P.E., S.E.                   E-mail: mtv(--nospam--at)skilling.com
Skilling Ward Magnusson Barkshire Inc.              Tel:(206)292-1200
1301 Fifth Ave, #3200,  Seattle  WA 98101-2699      Fax:        -1201

-----Original Message-----
From: David Adie [mailto:dadie(--nospam--at)bjginc.com]
Sent: Thursday, June 28, 2001 1:16 PM
To: 'seaint(--nospam--at)seaint.org'
Subject: RE: perforated shear walls - seismic design manual - volume 2


Perforated shearwall approach allows you to use skinny segments of
solid
wall when you otherwise would be prohibited due to the aspect
ratio-that is
its benefit.

is that right?  my apa report (dated april 2000) defines a perforated
shearwall segment as "a section of shearwall with full height
sheathing and
which meets minimum aspect ratio requirements in the governing
building
code".  it also states that "a perforated shearwall segment of minimum
length must be located at each end of a perforated shearwall".

i agree that there can be skinny segments in the interior portion of
the
wall, but their lengths can't be included in the summation of
shearwall
segments - right?

am i missing something here?

hago
da


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********