Check the minimum concentrated load used in original design.  For example, a
lobby in an office building requires a 2000 lb minimum concentrated load per
ASCE 7-95.  (The concentrated load is actually spread over a 2.5' square.)  

Maybe the original design accomodates your loading.  If not, you will need
to check the entire pathway that the equipment will travel within the
facility to arrive at its final location.  For this occurenc, you might be
able to restrict the live loading along path.  

In the final location, I doubt seriously that you would be able to restrict
the live loading.  At this point, I'd say you would have to analyze every
member in the load path (slab to beam to column).  You need to make it
absolutely clear that the equipment shall remain in the final position.
(Maybe anchor it so that it is less likely to happen.)
 

-----Original Message-----
From: Mitchell J. Sklar [mailto:MJS(--nospam--at)bala.com]
Sent: Tuesday, July 17, 2001 2:58 PM
To: seaint(--nospam--at)seaint.org
Subject: Distributed Floor Loads


What is the general rule or any published documents about checking an
existing floor for new loads. 

Example new UPS or Battery Cabinet installed in an existing building.
Assume original building live load design is 50psf + 20psf for
partitions. Battery Cabinet footprint is 45" x 32", weight = 3765#

Option 1 Gross load = 3765# / (45*32/144) = 376.5 psf (too much)
Option 2 3765# / [(18+45+18)*(18+32+18)]/144 = 98.4 psf (better)

How much area can I spread my new units out? 1 ft, 2ft?

Okay, now here is the twist, the Battery Cabinet is supported by 8
wheels @ 471#. How would you handle the concentrated stress?

Mitchell J. Sklar, P.E.
Structural Engineer
mjs(--nospam--at)bala.com
Bala Consulting Engineers, Inc.
p 610-649-8000 x 345
f  610-649-8475



* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 

* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org