The AISC bearing calculations are a check on a connected material limit
state, elongation of the bolt hole.  They are based on late 1970's
research.  The AISC "block shear" calculations are a check on a different
connected material limit state, fracture of the material.  They are based
on 1970's research.  AISC specification(s) consideration of both limit
states coincides with the time period when the profession was switching
from common bolts to high strength bolts, concentrating the same design
forces into a more compact area of the connected material.

Rick Drake, SE
Fluor Daniel, Aliso Viejo, CA

****************************



                                                                                                                   
                    "Peder Golberg"                                                                                
                    <peder@jgpierso      To:     <seaint(--nospam--at)seaint.org>                                               
                    n.com>                                                                                         
                    11/09/01 01:49       cc:                                                                       
                    PM                                                                                             
                    Please respond       Subject:     Re: Slip Critical Connections.                               
                    to seaint                                                                                      
                                                                                                                 . 
                                                                                                                   




Since oversized holes are allowed in slip critical connections, why does
bearing need to be checked when the hole is oversized?  How or what exactly
is being checked?   The requirements to "always check bearing"  were added
in the 8th edition of the AISC ASD manual and the earlier codes stated
"bearing does not need to be checked".   Is checking bearing meant to check
block shear type requirements.  What failures prompted the change?

Peder Golberg
Portland, OR

----- Original Message -----
From: <Rick.Drake(--nospam--at)Fluor.com>
To: <seaint(--nospam--at)seaint.org>
Sent: Friday, November 09, 2001 12:58 PM
Subject: Re: Slip Critical Connections


>
> Slip-critical connections must always be checked for bearing.
>
> The 1999 LRFD Specification, Section J3.10, requires that "Bearing
strength
> shall be checked for both bearing-type and slip-critical connections."
>
> The 1993 LRFD Specification, Section J3.10, requires that "Bearing
strength
> shall be checked for both bearing-type and slip-critical connections."
>
> The 1989 ASD Specification Commentary, Section J3.7, suggest that
requires
> that "slip-critical connections ... should comply with the provisions of
> Sect.s J3.4 (allowable tension and shear) and J3.8 (minimum spacing) to
> insure the usual minimum factor of safety of 2 against complete
connection
> failure."
>
> Regards,
>
> Rick Drake, SE
> Fluor Daniel, Aliso Viejo, CA
>
> ************************
>
>
>
>
>                     "Travis"
>                     <travis@jgpiers      To:     "seaint.org"
<seaint(--nospam--at)seaint.org>
>                     on.com>
>                     11/09/01 11:35       cc:

>                     AM
>                     Please respond       Subject:     Slip Critical
Connections.
>                     to seaint
>
.
>
>
>
>
>
>
>
> Is there any situation where the design of a slip critical  bolted
> connection would not be required to address bearing  requirements?
>
>
>
>
>
>
--------------------------------------------------------------------------
---------------------------
> The information transmitted is intended only for the person
> or entity to which it is addressed and may contain confidential
> and/or privileged material. If you are not the intended recipient
> of this message you are hereby notified that any use, review,
> retransmission, dissemination, distribution, reproduction or any
> action taken in reliance upon this message is prohibited. If you
> received this in error, please contact the sender and delete the
> material from any computer.  Any views expressed in this message
> are those of the individual sender and may not necessarily reflect
> the views of the company.
>
--------------------------------------------------------------------------
-----------------------------
>
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********





-----------------------------------------------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain confidential
and/or privileged material. If you are not the intended recipient 
of this message you are hereby notified that any use, review,
retransmission, dissemination, distribution, reproduction or any
action taken in reliance upon this message is prohibited. If you 
received this in error, please contact the sender and delete the 
material from any computer.  Any views expressed in this message
are those of the individual sender and may not necessarily reflect 
the views of the company.  
-------------------------------------------------------------------------------------------------------


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********