Jim,

Thank you very much.

Brian

-----Original Message-----
From: Jim Kestner [mailto:jkestner(--nospam--at)somervilleinc.com]
Sent: Thursday, February 21, 2002 3:38 PM
To: 'seaint(--nospam--at)seaint.org'
Subject: RE: Fire Rating


I asked a similar question awhile back on the list server, but I did not
get any response. I emailed UL directly and within a few days, I got an
official interpretation from them. Here is how I understand it:

The 8x28 was the actual beam that was tested in the particular assembly.
Other beam sizes may be substituted, but the spray on thickness has to be
adjusted according to a formula found on page 9 of UL 2001, Vol One.
W/D values of the substitute beam shall not be less than 0.37.
	W = weight of the beam in lbs/ft
	D = perimeter of protection in inches
	(I believe a W8x10, Case A, AISC pg 1-143, 8th edition, corresponds to a
W/D of 0.37.)
T1, adjusted fireproofing thickness is not less than 3/8".
the unrestrained beam rating is not less than one hour.
This adjustment procedure cannot be used for restrained beam ratings.

If you want to contact UL .......here is their website.

http://www.ul.com/

I hope this helps!

Jim Kestner

-----Original Message-----
From:	Brian K. Smith [SMTP:smithegr(--nospam--at)bellsouth.net]
Sent:	Thursday, February 21, 2002 3:01 PM
To:	seaint(--nospam--at)seaint.org
Subject:	Fire Rating

	I think this has been discussed before; however, I do not remember the
outcome.  I have a partial garage (one row of parking) under the main floor
of an office.  When we began the project, there was no need to fire rate
the
floor between the two.  Now that it is permit time, we have to rate the
floor system separating the two.  My client has faxed over some cut sheets
from the U.L. manual (I do not have copies of the entire manuals).  The
particular system he chose requires a minimum floor beam size of W8x28.  My
beams are deeper, but not as heavy (short span).  What is U.L.'s criteria
for MINIMUM?  Is it depth, weight, flange size?

Brian K. Smith, P.E.


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********