Section 10.7.1 and 11.8.1 of the 2002 318 code give a definition of deep
beams.  Section 11.8.1 pertains to the "shear" definition.  It states:

"The provisions of 11.8 shall apply to members with clear spans, ln,
equaly to or less than four time the effective beam height, h, or portions
of beams loaded with concentrated loads within 2h from the support that
are loaded on one face and supported of the opposite face so that
compression struts can develop between the loads and supports."

I had thought that the intent of adding Appendix A was to get an alternate
design method into the code, but that the older method would still be
permitted.  It appears, however, that the 2002 code doesn't specfically
include the old method that was part of the 1999 code.  Section 11.8.2
states:

"Deep beams shall be designed using nonlinear analyses as permitted in
10.7.1, or Appendix A."

It appears that the new "simplified" method in the 2002 code is to use the
provisions in Appendix A.

You can pose this question to ACI.  While you will get an answer to your
technical inquiry, it will not be an "official" code interpretation unless
wanted do an official request for interpretation from the committee, which
generally costs money and takes time (it has to be run through the full
standardization process of ACI like it was an actual code change
proposal).  There is a form on the ACI web page (www.aci-int.org) for
submitting a technical inquiry or you can send it to techinq(--nospam--at)aci-int.org.

HTH,

Scott
Ypsilanti, MI


On Wed, 27 Feb 2002, Edwin Schmeckpeper wrote:

> Does anyone have a copy of ACI 318-2002.  I have a question about the
> revised section 11.8 which covers Shear in Deep Beams.
>
> First, what is the definition of a Deep Beam for shear ?
>
> Second, is there a "simplified" method for calculating V_c for deep beams
> (in ACI318-99 you could assume that V_c was 2(f'c)^.5 * b * d ),
> or are you required to use the Strut-and-tie method ?
>
>
> Thanks
>
> Ed Schmeckpeper
> Department of Civil Engineering
> University of Idaho			E-Mail : eds(--nospam--at)uidaho.edu
>
>
>
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********