Keith:

Here are some guidelines that I use:

The maximum outside diameter of conduit, embedded into structural slabs,
shall not exceed 1/3 of the slab thickness (above the metal deck) nor the
clear distance between the top and bottom layers of reinforcing bars. When
conduit crosses in the slab, the maximum outside diameter shall not exceed
1/6 of the slab thickness (above the metal deck) nor the clear distance
between the top and bottom layers of reinforcing bars. Minimum clear
spacing between conduit shall not be less than one conduit diameter nor 3".

When conduit runs parallel with a composite beam, I do not allow them to
run the conduit tight to the studs.
I require a 12" minimun distance from the studs.

I hope this helps!

Jim K.

-----Original Message-----
From:	Roger Davis [SMTP:rdavis(--nospam--at)sdsarch.com]
Sent:	Thursday, February 28, 2002 1:44 PM
To:	seaint(--nospam--at)seaint.org
Subject:	RE: Opinions Please: Composite Beam/Deck Slab

See ACI 318 Section 6.3.  (Usually conduit about half the size they have
already placed is acceptable.)

Roger C. Davis
Architect
SDS Architects, Inc.


-----Original Message-----
From:	Keith Fix [mailto:kefix(--nospam--at)yahoo.com]
Sent:	Thursday, February 28, 2002 12:49 PM
To:	seaint(--nospam--at)seaint.org
Subject:	Opinions Please: Composite Beam/Deck Slab

Conduit has been laid on the deck.  Concrete has not yet been placed, but
is
scheduled to be placed tomorrow.  Are there conditions in which conduit
cast
horizontally in the plane of the slab is acceptable?

-Keith Fix, PE



__________________________________________________
Do You Yahoo!?
Yahoo! Greetings - Send FREE e-cards for every occasion!
http://greetings.yahoo.com

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********