Joseph,

	This is a different question.  Robert clearly indicated that he had
vertical and horizontal stirrups to accommodate shear and he asked if
these bars could also be used as flexural reinforcing.  My answer was
that he could use the same bars for both purposes provided that he added
the required amounts together and detailed them appropriately.

	Robert did not indicate whether he was accommodation the loading from
the retained earth with bars spanning horizontally or with bars spanning
vertically (or for that matter with a two way action, hence, with bars
spanning in both directions).

	Other than that I agree with you, Joseph. I would normally expect the
primary shear reinforcing to be horizontal and the primary bending
reinforcing to be vertical but we don't know all of the details of the
design problem.

				Regards,

				H. Daryl Richardson

Joseph R. Grill, PE wrote:
>
> Isn't shear reinforcing in a shear wall the horizontal reinforcing?  See
> example 23.4 Notes on ACI 318-95.  Therefore, (simplified viewpoint) the
> vertical and horizontal bars are not acting for both purposes.
>
> Joseph R. Grill, PE
>
> -----Original Message-----
> From: Daryl Richardson [mailto:h.d.richardson(--nospam--at)shaw.ca]
> Sent: Thursday, March 14, 2002 10:19 AM
> To: seaint(--nospam--at)seaint.org
> Subject: Re: Concrete Shear Wall Below Grade; In-Plane / Out-of-Plane
> Behavior
>
> Robert,
>
>         It is my understanding that you can use the SAME BARS for both
> purposes
> but that you must provide sufficient total area of steel such that
>
> As(total) = As(bending) + As(shear)
>
> at all critical locations.  You must also detail the bars to accommodate
> both purposes.  If the bending action is two directional (which I don't
> expect to be the case) then the above would apply in both directions.
>
>         I hope this helps.
>
>                                 Regards,
>
>                                 H. Daryl Richardson
>
> > Rogers, Robert wrote:
> >
> > To all those informed concrete designers out there.....here's a question
> > for you........(an item of discussion & debate)
> >
> > Deep, reinforced concrete basement shear wall which is also
> > experiencing out-of-plane loading from the soil.  Shear wall design
> > indicates the need for horizontal and vertical stirrups as well as
> > flexural steel in either end of the shear wall.  The vertical stirrups
> > act as shear reinforcement to resist the in-plane shear load.  Can
> > these same stirrups be used as flexural reinforcement for the
> > out-of-plane loading from the soil ?  Not addressed in the PCA Notes
> > on ACI 318-99 and have found nothing in three textbooks addressing the
> > issue.
> >
> > Thanks
> > Robert
> >
> > Robert C. Rogers, PE
> > Senior Structural Engineer
> > A.M. Kinney, Inc.
> > Consulting Engineers / Architects
> > 150 East Fourth Street, 6th Floor
> > Cincinnati, Ohio 45202
> > PH: 513-421-2265, ext. 125
> > FX: 513-345-1318
> > rogersr(--nospam--at)amkinney.com
> > www.amkinney.com
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********