Greg,
I can think of two issues for this type of bracing:
1- The unbalanced load of the single brace needs to be
transferred through the beam. So you will end up with a
heavy beam section.
2- There are limits on the percentage of the seismic load
that can be resisted by tension-only/compression-only
braces. So you may want to make sure that there are other
braces in the system to act in the opposite direction.
Hope it helps,
Frank

--- Greg Meyer <gmeyer(--nospam--at)scahouston.com> wrote:
> Scott, Thanks for your input.  It would just be a single
> brace member.
> Essentially what I have is 1/2 of a inverted "V" chevron
> brace.
> I guess that it would fit the criteria of  UBC 2213.8.4.3
> Nonconcentric
> bracing.
> 
> Greg
> 
> -----Original Message-----
> From: Scott Maxwell [mailto:smaxwell(--nospam--at)engin.umich.edu]
> Sent: Tuesday, July 23, 2002 2:17 PM
> To: 'seaint'
> Subject: Re: steel brace
> 
> 
> Greg,
> 
> Based upon your limited description, I would say yes you
> can use this type
> of brace, but a little more information would be helpful.
> 
> Is there another brace that meets this one at the middle
> of the beam
> coming from the beam to column connection at the other
> side of the beam?
> 
> If so, does the working point of the braces (essentially
> the centerlines)
> meet roughly at the centerline of the beam?
> 
> If the answer to the first question is "no", then it
> sound like an
> eccentric brace system.
> 
> If the answer to the first and second question is "yes",
> then is sounds
> like a concentric brace system.
> 
> If the answer to the first question is "yes" and the
> second is "no", then
> it sounds like another configuration for an eccentric
> brace system.
> 
> FYI, an eccentric brace system relies on getting its
> brace force into a
> beam or column by both bending and resolution of the
> axial loads into
> component forces (like a truss member), in general terms.
>  An eccentric
> brace system will have a "link" beam segment that is
> designed to create
> the ductility in the system (note an eccentric brace
> system is typically
> more ductile than a concentric brace system).  A
> concentric brace system,
> OTOH, will not rely on any bending to transfer force from
> the brace to
> beam or column.
> 
> HTH,
> 
> Scott
> Ypsilanti, MI
> 
> On Tue, 23 Jul 2002, Greg Meyer wrote:
> 
> > 	I would like to use a brace that goes from a beam to
> column connection at
> > one level to the middle of a beam at the next level.
> > The brace would be part of the lateral resisting system
> for a building
> > located in a seismic zone 3  (1997 UBC).
> > It doesn't seem to meet any of the definitions for
> braces in the UBC.
> >
> > Can I use this type of brace?
> >
> > If I can, how would this brace be classified?
> (Eccentric, Concentric, etc)
> >
> >
> > Thanks in advance,
> >
> > Greg Meyer
> >
> >
> > ******* ****** ******* ******** ******* ******* *******
> ***
> > *   Read list FAQ at:
> http://www.seaint.org/list_FAQ.asp
> > *
> > *   This email was sent to you via Structural Engineers
> > *   Association of Southern California (SEAOSC) server.
> To
> > *   subscribe (no fee) or UnSubscribe, please go to:
> > *
> > *   http://www.seaint.org/sealist1.asp
> > *
> > *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any
> email you
> > *   send to the list is public domain and may be
> re-posted
> > *   without your permission. Make sure you visit our
> web
> > *   site at: http://www.seaint.org
> > ******* ****** ****** ****** ******* ****** ******
> ********
> >
> 
> 
> ******* ****** ******* ******** ******* ******* *******
> ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server.
> To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any
> email you
> *   send to the list is public domain and may be
> re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ******
> ********
> 
> 
> ******* ****** ******* ******** ******* ******* *******
> ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> * 
> *   This email was sent to you via Structural Engineers 
> *   Association of Southern California (SEAOSC) server.
> To 
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any
> email you 
> *   send to the list is public domain and may be
> re-posted 
> *   without your permission. Make sure you visit our web 
> *   site at: http://www.seaint.org 
> ******* ****** ****** ****** ******* ****** ******
> ******** 


=====
Fariborz Tehrani,                      Phone: (310)801-4237Professional Civil Engineer              Fax: (877)743-6206BSCE, MSCE, PE                    Voice Mail: (877)743-6206email: general@fmtehrani.comweb: www.fmtehrani.com

__________________________________________________
Do You Yahoo!?
Yahoo! Health - Feel better, live better
http://health.yahoo.com

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********