In answer to the question below, I have the following courtesy of my fire
engineering colleague Farid Alfawakhiri here at AISC.

Charlie

********************
Open parking structures category is recognized by all model codes in the US.
For non-combustible construction, no fire protection (0 hours rating) would
be required, if the following limits are observed

IBC : 50,000 sq.ft area per tier (max) ; 8 tiers (max) ; 2 sides (min) open
20 % (min) of wall area of entire perimeter
NBC : 50,000 sq.ft area per tier (max) ; 8 tiers (max) ; 2 sides (min) open
40 % (min) of wall area of entire perimeter
SBC : 400,000 sq.ft area per tier (max) ; 8 tiers (max) ; 2 sides (min) open
50 % (min) of wall area of open sides
UBC : 30,000 sq.ft area per tier (max) ; 8 tiers (max) ; 2 sides (min) open
20 % (min) of wall area of entire perimeter

Note that while IBC, NBC and UBC have a significantly lower value than SBC,
IBC, NBC and UBC allow unlimited area for non-combustible unprotected (0
hours rating) open parking structures if 50% (min.) of the wall area on all
sides is open, the distance from any point on the floor is within 200 ft to
the nearest opening, and the height of the structure is within 75 ft.

Please note that these liberal limits are in recognition of the very low
fire hazard levels in open parking structures, mainly due to good
ventilation. These rules do not apply to closed parking.

________________________

Farid Alfawakhiri, Ph.D.
Senior Engineer, Fire Design
312-670-5441 (phone)
312-644-4226 (fax)
alfawakhiri(--nospam--at)aisc.org
 
American Institute of Steel Construction, Inc.
One East Wacker Drive, Suite 3100
Chicago, IL 60601-2000
_____________________________________
 

-----Original Message-----
From: Carter, Charlie 
Sent: Wednesday, January 29, 2003 05:54
To: Alfawakhiri, Farid
Subject: FW: Fire ratings to UBC 1997


Please help me answer this. You have to be a subscriber to post messages to
the SEAINT list serv, so send it to me and I will post it.

Charlie

-----Original Message-----
From: Mark Geoghegan [mailto:structuraltech.vsl(--nospam--at)verizon.net]
Sent: Tuesday, January 28, 2003 7:35 PM
To: seaint(--nospam--at)seaint.org
Subject: Fire ratings to UBC 1997


I need some assistance/comments with the following:

4 level parking structure, open on all 4 sides, approx 22,000 SF per floor,
PT concrete flat plate construction. Stand alone parking structure, no
structure above, none adjacent. Structure is 25 years old.

To UBC 1997 its Use and Occupancy is GROUP S,  Division 4, Open Parking
Garage.

Based upon the Use and Occupancy and Floor Area and Building Height I have
determined it is Type II-N construction (correct?).

It is up for repair/strengthening - if structural steel or other external
strengthening systems are selected as a repair/strengthening option to
support the concrete slabs, does the external strengthening system need to
be fire protected? Or does it just have to be "non-combustible" materials?

I say no fire protection is required because it is Type II-N - but I welcome
comments.

Many thanks

Mark Geoghegan
Honolulu, HI



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********