Kenny,

I've also struggled with this section of the code.  The conclusions that
I've reached are as follows:
1.  fa<.04fm'  OK to use strength design and slender wall analysis.
2.  fa>.04fm' and h/t<30  OK to use strength design and slender wall
analysis with deflection limitation.
3.  fa>.04fm' and h/t>30  Need to use ASD design and the analysis of forces
are to include "slenderness effects" (P-delta, variable moment of inertia
and load duration effects).

The 2000 IBC has raised the stress ratio limit to .05fm'.  The original
limit seemed arbitrary and indeed it is.  The limit was imposed because the
testing that validated the design procedure was modeled for light roof
loads.  Perhaps when new testing is performed, the design provisions can be
extended.

I hope this was helpful.

Curt La Count
Jacobs Engineering
Portland, OR

-----Original Message-----
From: Kenny Yip [mailto:kenny(--nospam--at)jeiwa.com]
Sent: Tuesday, March 04, 2003 4:26 PM
To: seaint(--nospam--at)seaint.org
Subject: CMU Wall Design for Out-of-Plane Loads


I posted the following question last Wednesday or Thursday, but so far no
one has ever responded it.  I think my question must be a challenging one.
I post it here one more time to see if I can be of any luck.

Dear Fellow Engineers:

Under section 2108.2.4.4 of 97UBC, there are seven equations (from 8-19 to
8-25) associated with walls having axial load of 0.04fm' or less.  I am
wondering if this set of formulas can be equally applied to the next
section (i.e. 2108.2.4.5) for walls with axial load between 0.04fm' and
0.2fm' and the slenderness ratio h/t does not exceed 30.  No equations,
other than (8-26), are given in this section.

My axial stress is 135 psi under service load (my fm' = 2500 psi), and h/t =
18.5.  I have talked to some engineers.  Some said that I can use those
equations and some told me that I can not use them.  What do you think?

I appreciate your informative advice.


Kenny Yip, P.E.
Jones Engineers
Bellingham, WA


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 


==============================================================================
NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient.  Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited.  If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.

==============================================================================


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********