Need a book? Engineering books recommendations...

Return to index: [Subject] [Thread] [Date] [Author]

RE: Parking Garage Loading - IBC/UBC

[Subject Prev][Subject Next][Thread Prev][Thread Next]
I saw someone ask about how I calculated the loads in the IBC last night, but didn't have the opportunity to answer.  Well, here are the calcs:
 
Per IBC section 1607.9.2:
 
Double-tee: trib area = 9'x54'=486ft^2,
    R=0.08%*(486-150) = 26.88%,
    LL=(100%-26.88%)x50 PSF = 36.56 PSF
 
Center Inverted-Tee: trib area=27'x54'=1458ft^2
    R=0.08%*(1458-150) = 104.64% > 40%, therefore R=40%
    LL=(100%-40%)x50 PSF = 30 PSF
 
Column: trib area > trib area for IT which already has R > 100%, therefore R=60%
    LL=(100%-60%)x50 PSF = 20 PSF
 
You will notice that the limit of section 1607.9.1.2 does not apply to section 1607.9.2.  Whether intentional or not, that is how it is written.  That may not be the intent, but that is part of the reason I asked the question in the first place.
 
Hope that clarifies things a little.
 
Jake Watson, P.E.
Salt Lake City, UT