James,

It depends on what your masonry "framing element" is.  Let's take the
example of a one story structure with no windows or opennings in the
masonry wall.  Assuming the wall spans vertically.  The effective area, in
my understanding, would be the vertical span times the width of the entire
wall (width being between corners or openings).

If we take an example of a line of "punched" windows in the wall, where
horizontally between the windows the wall spans vertically with the small
pieces of masonry vertically between the windows spanning horizontally.
Then you would use an area of width of the wall times the wall height
(span) to determine the wind load for the masonry that spans vertically
(since the vertical spans still carry the load from the horizontal spans
and the windows as reactions from the horizontal masonry and the windows).
And for the horizontal masonry, teh area would be the width of the window
times the vertical distance from center of window to the center of the
next window (the horizontal span still carries the wind load from the
window, unless the windows are designed to "span" horizontally).

The end result is that you need to look at what you are considering as
your masonry structural element and what portion of the wind that element
is carrying as a tributary load.

HTH,

Scott
Ypsilanti, MI


On Wed, 16 Apr 2003, Cory Structural Engineering, P.C. wrote:

>
> What effective wind area should be used for concrete masonry unit wall
> design per figure 6-3 of SEI/ASCE 7-02.  Should it be vertical wall
> reinforcing spacing times wall height which would give a high
> pressure?   For a 15'-0" high wall I am contemplating installing a bond
> beam at mid-height which should increase the effective wind area and allow
> designing for a lower pressure.  Is it reasonable to assume that the joint
> reinforcing would make the wall act as a unit such that the effective wind
> area would be the wall height times its length.  Does anyone have any
> recommendations for effective wind area?
>
> James a. Cory III, P.E.
> Cory Structural Engineering, P.C.
>
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********