RE: minimum fc for Residential slab on grade

[Subject Prev][Subject Next][Thread Prev][Thread Next]
Title: Message

Is “Deputy Inspection” special inspection ???

 

Special inspection per section 1701.5 is not required, per the exceptions, for foundations for Group R occupancies, f’c NOT GREATER than 2500 psi, nonstructural slabs on grade, and site work fully supported on earth.

 

-gerard

Santa Clara, CA

 

-----Original Message-----
From: Dennis Wish [mailto:dennis.wish(--nospam--at)verizon.net]
Sent: Wednesday, July 09, 2003 2:28 PM
To: light_framing(--nospam--at)structuralist.net
Cc: seaint(--nospam--at)seaint.org
Subject: minimum fc for Residential slab on grade

 

I designed a single story residence (spec home but large) using a slab on grade which is typical in this area. Historically, we placed f'c=2,000 psi concrete for everything but where proprietary frames such as Hardy Frames are used. The typical soil in the area is silty sand with a bearing pressure of 1,500 psf and with increases allowed for depth and width.

I received a plan check correction based on the 1998 CBC and 1997  UBC. He quoted section 1921.2.4 which requires high strength concrete but has an exception that allows for concrete not less than 2,500 psi. This is generally required when inspection of the concrete is called for and not for simple slab on grades. The city has, during the 1997 UBC cycle allowed for f'c=2,000 psi concrete, but the contract plan check company requires 2,000 psi concrete so as not to force deputy inspection.

 

Are there any comments as how I should address the plan check correction since deputy inspection can be expensive and there are no problems with subsidence or expansive soils in the area.

 

Am I wrong on this one????? If so, it comes as a surprise.

 

Thanks

Dennis