Need a book? Engineering books recommendations...

Return to index: [Subject] [Thread] [Date] [Author]

RE: Fireproofing

[Subject Prev][Subject Next][Thread Prev][Thread Next]

I thought I’ve seen fireproofing weighing anywhere from 15 pcf up to 40 pcf (Grace FP Products).  Assuming a W18x35, surface area (minus top of top flange) = 4.34 sf/ft (AISC Manual).  For each inch of FP, weight of FP = 5.5 plf to 14.5 plf.  Depending on how much FP, average weight is probably at most in the 2 to 3 psf range and I generally lump that into the “Miscellaneous” load.  Special situations might require a closer look.

 

-----Original Message-----
From: Paul Feather [mailto:pfeather(--nospam--at)SE-Solutions.net]
Sent: Wednesday, August 27, 2003 10:38 AM
To: seaint(--nospam--at)seaint.org
Subject: Re: Fireproofing

 

practically zero.  If the spray on fire protection is more than two or three pounds per linear foot on a 24" beam I would be surprised.  Typically spray on is accounted for in the miscellaneous loading.  If the spray on is a factor in the beam design, you are cutting things way too close. :-)

 

 

----- Original Message -----

Sent: Wednesday, August 27, 2003 5:57 AM

Subject: Fireproofing

 

Anybody got a good rule of thumb uniform dead load for sprayed on fireproofing of steel beams?

 

D. Matthew Stuart, P.E., S.E., P.Eng.

Senior Project Manager

Schoor DePalma Engineers and Consultants

Manalapan Structural Department

200 State Highway Nine

Manalapan, NJ 07726

732-577-9000 (Ext. 1275)

908-309-8657 (Cell)

732 -431-9428 (Fax)

mstuart(--nospam--at)schoordepalma.com