RE: Effective Section - ACI 318

[Subject Prev][Subject Next][Thread Prev][Thread Next]
I think to answer the original question succinctly:

The values are derived from the results of frame tests and analyses and
include an allowance for the variability of the computed deflections.
Additional references should abound when one performs a keyword search
using Moment of Inertia, Concrete, Frame, and Analysis on a scientific
database (such as CEBD, Compendex, etc.) available at most university
libraries.

The only other thought I would add is that the values listed in ACI
10.11.1 are intended for use in both first-order strength-level elastic
analysis and 2nd order strength-level analysis (P-Delta or Mag. Moments)
unless more detailed analysis is performed.  

Robert C. Rogers, PE


-----Original Message-----
From: Scott Maxwell [mailto:smaxwell(--nospam--at)engin.umich.edu] 
Sent: Tuesday, September 02, 2003 12:14 PM
To: seaint(--nospam--at)seaint.org
Subject: Re: Effective Section - ACI 318


These values for the "effective" moment of inertia are only used in
section 10.11.1 of the ACI 318-02 code (at least to my knowledge).  They
are listed as "permitted" values to be used when doing second-order
(i.e. magnified moments) analysis, but are also generally used as a
reasonable approximation (depending on loading level) when doing general
analysis of frames for things like deflections and other serviability
requirements (there is a similar recommendation for moment of inertia
values in an ACI publication for analyzing two-way flat plate systems
for lateral loads when using the equivalent frame method).

Now as to where they come from...just take a look at the commentary for
section 10.11.1.  It stateds:

"The moments of inertia were taken as 0.875 times those in Reference
10.28."

And reference 10.28 is MacGregor, J.G., and Hage, S.E., "Stability
Analysis and Design Concrete," Proceedings, ASCE, V. 103, No. ST 10,
Oct. 1977.

With regards to use of these values during service loads checks, the
commentary further comments:

"The magnified service loads and deflections by a second-order analysis
should also be computerd using service loads.  The moments of inertia of
the structural members in the service load analysis should, therefore,
be representative of the degree of cracking at the various service load
levels investigated.  Unless a more accurate estimate of the degree of
cracking at design service load level is available, it is satisfactory
to use 1/0.70 = 1.43 time the moment of inerita given in 10.11.1 for
service load analyses."

Thus, it would appear the intent of the ACI 318 code is that the moment
of inertia values that you cited are meant as an alternative to a more
detailed determination for use in second-order strength analysis/design
applications.  If you then want to use those values to do a second order
analysis for the purposes of determining say deflections, then you
actually should multiple those values by 1.43.

Now, I would also surmise that to some degree, those values are meant to
be an "average" set of values that reflect a large range effective
moment of inertia values that depend largely on to what degree the
concrete has cracked.  In otherwords, they are likely meant to be a
conservative value that can easily be used if you don't want to spend
the time and effort to do a more detailed determination of the degree of
concrete cracking and the associated effective moment of inertia.

HTH,

Scott
Ypsilanti, MI


On Mon, 1 Sep 2003, Prof. A R Chandrasekaran wrote:

> Dear Friends,
>
> I would be thankful if some of you could explain the background to the

> clause of ACI as quoted below:
>
> The specifications of ACI 318 RM - 02 for moment of
> inertia of members are
> ------------------------------------------
> beams    0.35 Ig (gross moment of inertia)
> columns  0.70 Ig
> walls uncracked 0.70 Ig    cracked  0.35 Ig
> Flat slabs and flat plates   0.25 Ig
> --------------------------------------------
> Is it based on analytical/experimental research or is it empirical ? 
> Could you suggest any References for me to become more familiar with 
> this topic ?
>
> I have some experience of system identification studies - trying to 
> fit analytical model to match experimental results. In particular for 
> a RCC framed structure (TG framed foundation) we carried out extensive

> experiments after the structure was built and operated under actual 
> loads. The structure was analysed as a space frame as well as by using

> 3D solid finite elements. The gross section of the concrete was used 
> with static modulus of elasticity.
> The best fit was obtained when using an effective factor of 0.65. In
one
> sense, ACI 316 gave us confidence that the effective factor should be
less
> than unity but it was not possible to assign different factors for
beams and
> columns
> to confirm ACI values. 3D analysis could predict frequencies and mode
shapes
> near the operating range of frequency (50 Hz) and space frame analysis
could
> not do so.
>
> Thanks.
> A R Chandrasekaran
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********