I think you could have developed some kind of preliminary conservative
reactions to design your foundations around in the time it took to write
your email!

Some manufacturers have software that they make available for
preliminary sizing of reactions for standard building configurations at
no cost (Contact ABC in Dothan, AL).

In either case just indicate on the CD that the foundations should not
be cast until the actual reactions are provided by the selected vendor
and educate your client that some re-design may be required at that
conjuncture (read add service) or be sure to include such an effort in
your fee.

D. Matthew Stuart, P.E., S.E., P.Eng.
Senior Project Manager
Schoor DePalma Engineers and Consultants
Structural Department
200 State Highway Nine
Manalapan, NJ 07726
732-577-9000 (Ext. 1275)
908-309-8657 (Cell)
732 -431-9428 (Fax)
mstuart(--nospam--at)schoordepalma.com

-----Original Message-----
From: Sherman, William [mailto:ShermanWC(--nospam--at)cdm.com]
Sent: Thursday, November 06, 2003 3:56 PM
To: 'seaint(--nospam--at)seaint.org'
Subject: Building Code Complexity

This email is submitted for general comments on building code
complexity.
(Comments on specific code requirements are also welcome.)

I have been developing design requirements for a single story
pre-engineered
metal building for a water treatment plant in New England. The structure
is
intended to be a concentrically braced steel frame for lateral loads,
although rigid moment frames will be used to resist vertical loads. The
lateral bracing is intended to avoid seismic requirements for moment
frames
resisting earthquake forces. Although we have requested preliminary
foundation reactions from local pre-engineered metal building suppliers,
they will not provide this information for "free". Although we would be
willing to pay for a preliminary design, legal counsel has said that if
we
pay a supplier for a design, that supplier should be excluded from
bidding
as they would have a competitive advantage over other bidders (for a
public
works project). Thus we plan to develop our own preliminary design to
get
foundation reactions.

Developing the required design load cases has been a lesson in building
code
complexity. The governing building code is the 2000 IBC. The building is
an
L-shaped building and will have non-symmetrical bracing and irregular
bay
sizes, due to equipment layout. I have currently come up with a
"minimum" of
83 load cases to be evaluated! (I guess I can understand why the
building
manufacturers no longer want to design for free.)


FYI, following is a summary of the code requirements.

Seismic Design:

Basic Seismic Design Parameters per IBC 2000:
        - Seismic Use Group III, Importance Factor = 1.50 (per IBC Table
1604.5, required for fire suppression)
        - Site Class D (based on Soil Profile, per Geotech Report and
IBC
Table 1615.1.1)
        - Sds = 0.401; Sd1 = 0.163 (based on zip code)
        - Seismic Design Category D (per IBC Tables 1616.3(1)&(2))

Per IBC Section 2212.1.2, the steel structure must conform with AISC
Seismic
Provisions, Part I (LRFD) or Part III (ASD).

It is proposed to use AISC Seismic Provisions Part I, Section 14.5 for
Low
Buildings (recommended by a building manufacturer). Members and
connections
are to be designed for Load Combinations 4-1 and 4-2 (with overstrength
factors), as given in Section 4.1 of Part I. It should also be noted
that
Part III for Allowable Stress Design uses the same load combinations, so
these may be used for LRFD or ASD. In these equations, the required load
factor for seismic (omega-zero) is 2.0 (i.e., 2.0E is used). Orthogonal
effects need not be considered with these load combinations. However,
standard load combinations using 1.0E must also be analyzed, including
orthogonal effects. Thus, there are 2 standard load combinations and 2
special load combinations for seismic effects.

Note: Where Allowable Stress Design is used in accordance with Part III
of
the AISC Seismic Provisions, allowable stresses must be factored up by a
factor of 1.7 and then multiplied by a resistance factor which varies by
type of stress and component (e.g., flexure vs shear, tension vs
compression, welds vs bolts, etc). ASD load combinations include the
same
load factors as for LRFD. Thus in effect, the same analysis is performed
for
LRFD and ASD but different formulas are used for effective strengths.
One
effect of this is that standard allowable stress design checks built
into
software for ASD design, cannot be used directly since the varying
resistance factors have not been incorporated. Thus member design must
be
done manually from the analysis results for forces and stresses, when
ASD is
used. However, if the software includes LRFD code requirements, that may
be
used for member design. (I guess AISC will succeed in forcing LRFD upon
us.)


Due to the L-shaped building, plan irregularities must be accounted for
in
accordance with IBC Table 1616.5.1. Type 1a or 1b irregularity must be
evaluated due to differential story drift at the long end of the
building vs
the short end of the building. Type 2 irregularity must be evaluated due
to
the re-entrant corner. (Type 5 irregularity may also apply due to
bracing
not being symmetrical about the major axes.)

IBC Table 1616.6.3 permits the equivalent lateral force method to be
used
"with dynamic characteristics included in the analytical model".
Equation
16-35 will be used to determine the seismic response coefficient (i.e.,
the
peak seismic response; Equation 16-36 does not govern based on the
estimated
period per 1617.4.2.1). Redundancy must be evaluated in accordance with
IBC
Section 1617.2.2. Torsion must be evaluated in accordance with IBC
Section
1617.4.4 (including torsion due to mass and stiffness distribution,
accidental torsion, and dynamic amplification of torsion). Where
orthogonal
effects must be evaluated, design must conform to IBC Section 1620.2.2.

Seismic effects should be evaluated in two directions for each
orthogonal
axis, to get the maximum tension and compression reactions at braces and
at
foundations. Furthermore, positive and negative accidental torsion
should be
evaluated for each of these cases. This results in 4 basic load cases *
2
axes * 2 directions * 2 torsion eccentricities = 32 load cases.
Additional
combined load cases must also be evaluated on a case-by-case basis to
account for orthogonal effects (such as where orthogonal braces attach
to a
single column base).

Story drift must be evaluated in accordance with IBC Table 1617.3 (max
allowable drift = 0.010*h) and Section 1617.4.6; but for drift the
redundancy coefficient should be equal to 1.0. If the redundancy
coefficient
calculated from IBC Section 1617.2.2 is greater than 1.0, additional
load
cases should be evaluated. It is proposed to select the most critical
cases
for building deformation from the original strength design load cases by
judgment and evaluate drift as needed.


Wind Design Parameters per IBC 2000:

Wind Load:
        - Design per ASCE 7-98, Chapter 6, Method 2 - Analytical
Procedure
        - Basic Wind Speed = 100 mph, Importance Factor = = 1.15
        - Exposure Category B (wooded area)
        - Topographic Factor, Kzt = 1.0

Note that this building is not a "simple diaphragm" building or "regular
shaped building" due to lack of symmetry. There are 3 basic load
combinations in the 2000 IBC including wind. However in accordance with
ASCE
7-98, cases with positive and negative internal pressures must be
considered
and, as shown in Figure 6-4 of ASCE 7-98, two cases must be evaluated
for
each of the four building faces (similar to "accidental torsion" for
seismic
design). This results in 3 basic load cases * 2 internal pressures * 4
faces
* 2 cases = 48 load cases.


Additional Basic Load Cases:

There are 3 basic load combinations to account for dead load, floor live
load, and roof snow load, without lateral wind or seismic loads.
Although
there are no "floor live loads" acting on our building frame, one bay
will
be affected by monorail loads. Also, collateral loads should be included
to
account for lighting and HVAC hanging from the ceiling.

Snow Design Parameters per IBC 2000:
        - Ground Snow Load = 50 psf, Importance Factor = 1.20
        - Terrain Category B, Partially Exposed, Thermal Factor = 1.1 at
process area and 1.0 at admin area
        - Roof slope varies 4:1 or 8:1 (14-deg to 7-deg)

For gable roofs, balanced and unbalanced snow loads must be evaluated
and
wind from all directions must be accounted for to determine unbalanced
loads. Thus 4 wind directions must be evaluated for unbalanced snow
conditions plus one full balanced snow load case, for 5 snow load cases.
However, the 4 unbalanced snow load conditions should be able to be
included
in wind load combinations already accounted for.


It appears that this single story steel building design will require 32
seismic load cases, 48 wind load cases, and 3 basic load combinations,
as a
minimum.

(For reference, for a rectangular building with symmetrical bracing, the
load cases could be reduced to 23: the seismic and wind load cases could
each be reduced by a factor of 4, including a factor of 2 by avoiding
torsional eccentricities in two directions for each case and a factor of
2
by avoiding loads in each direction for north-south or east-west load
cases.
Results for the most critical stresses on one side of the building would
be
used for the opposite side of the building.)


William C. Sherman, PE
CDM, Denver, CO
Phone: 303-298-1311
Fax: 303-293-8236
email: shermanwc(--nospam--at)cdm.com

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********

_________________________________________________________________
Crave some Miles Davis or Grateful Dead? Your old favorites are always playing on MSN Radio Plus. Trial month free! http://join.msn.com/?page=offers/premiumradio


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* * This email was sent to you via Structural Engineers * Association of Southern California (SEAOSC) server. To * subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
* Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you * send to the list is public domain and may be re-posted * without your permission. Make sure you visit our web * site at: http://www.seaint.org ******* ****** ****** ****** ******* ****** ****** ********