Thanks for the reply Steve. This is a situation where there is no rim
joists. The floor joists perpendicular to the cripple wall - unblocked.
The top plate of the cripple wall is a single plate as I think I
mentioned. The 2003 Existing building code does cover the conditions for
Rim Joists at the end of the floor joists - this is not the case. There
is a definite discontinuity unless you overlap the plywood and consider
the nailing of the panel as sufficient to continue the drag connection -
which does not make me comfortable. 
I think that since I have not had any other comments on this, I'll play
safe and block for a couple of bays to install strapping and take care
of the discontinuity. 

One final issue, the same code does not require porches that are on
cripple walls to be sheathed. In the case, the home has a porch that is
on cripple walls and columns. I see on of the reasons for this, while
the cripple wall may be saved by sheathing, the posts (the porch
cantilevers out from the home by about five feet) are not secured and
would fail. However, if the corners were strapped, there is a
possibility that the porch could be saved by restraining the columns
(6x6 posts penetrate the cripple walls at two corners) from lateral
movement - possibly enough to prevent them from overturning. However,
without the strapping and cripple wall sheathing, the cripple walls will
fail, bringing the columns with them.


Any comments on what others would do?

Thanks again Steve for your comments.

Dennis


Dennis S. Wish, PE


California Professional Engineer

Structural Engineering Consultant

dennis.wish(--nospam--at)verizon.net

http://www.structuralist.net

 


-----Original Message-----
From: Steve Privett [mailto:eqretrodr(--nospam--at)earthlink.net] 
Sent: Wednesday, March 31, 2004 7:11 AM
To: seaint(--nospam--at)seaint.org
Subject: Re: Cripple wall sheathing - need fast answer

Dennis,

If the rim joist is continuous, and not spliced at the same place as the

top plate, I don't worry about blocking and strapping at the top plate.

I do make sure that framing anchors are installed between the top plate 
and the rim joist and let the rim act as the splicing element.  When the

original construction does not have a continuous rim, I call out 
strapping at the top side of the top plate.  It requires slipping the 
strap under a few joists, but that's a simple task.

Steve P
Pasadena, CA
On 3/30/2004 2:50 PM after considerable forethought, Dennis Wish wrote:

>Hi,
>
>I have a home with a raised floor on an 18-inch cripple wall. The home
>is not braced and I am completing the details. One problem I ran into
is
>that the cripple wall has only a single top plate and the joists are
>placed above the studs rather than between joists. 
>
> 
>
>In the past, I have always blocked between the studs and strapped
across
>the discontinuity – however, the 2003 Existing Building Code figure
A3-1
>and similar figures identifies a single our double top plate but does
>not require correction.
>
> 
>
>Do I block and strap or not????
>
> 
>
>
>Dennis S. Wish, PE
>
>
>California Professional Engineer
>
>Structural Engineering Consultant
>
>HYPERLINK "mailto:dennis.wish(--nospam--at)verizon.net"dennis.wish(--nospam--at)verizon.net
>
>HYPERLINK "http://www.structuralist.net/"http://www.structuralist.net
>
> 
>
>
>---
>Outgoing mail is certified Virus Free.
>Checked by AVG anti-virus system (http://www.grisoft.com).
>Version: 6.0.572 / Virus Database: 362 - Release Date: 1/27/2004
> 
>  
>
>  
>


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 

---
Incoming mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.572 / Virus Database: 362 - Release Date: 1/27/2004
 

---
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.572 / Virus Database: 362 - Release Date: 1/27/2004
 


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********