You are right Peter. 
I just assumed we have the right design and we need 18" thick slab with
#7 @ 12". (which is not equivalent to 19" slab with 1.5% steel fiber) 
Definitely with having the right loads we may end up with totally
different answer.

-----Original Message-----
From: PeterSHiggins(--nospam--at)cs.com [mailto:PeterSHiggins(--nospam--at)cs.com] 
Sent: Thursday, June 17, 2004 11:52 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Steel Fibers Replacing Structural Reinforcing?


Perhaps this is a bit off the topic, but having designed many rack
supported buildings (including some very heavily loaded ones over 120'
tall), I have to ask: what are they storing which generates a load which
would require such a slab? Or is the soil really pathological?

For posts on roughly 8' centers both ways, and decent dirt, using even
rudimentary slab-plate/soil-halfspace methods, your design would be good
for at least 180 kips per post working load or 2,800 psf. Even at 120'
high, this is 23 pcf gross volume. I don't know of any rack supported
building with that sort of density. The pallet itself is usually this
value, and they're typically less than 1/4 of the total building volume
(the rest is mainly air). My personal record is less than 35 pcf of
reserved pallet volume (the actual pallet was 45-50 pcf including the
volume of the skid), and that one was only 85 ft tall for around 10-12
pcf of building volume.

Either your're sitting on a world record holder for density (by a very
wide margin), or someone's not computing the loads properly. I'd ask
them to recompute the design load and see if they forgot to divide by 2
somewhere, before I'd embark on such a monster slab for an ASRS
building.

Peter S. Higgins, SE

"A Miraftab" <seaosd(--nospam--at)hotmail.com> wrote:

> 
> 
> 
>Professor Bayasi in San Diego State University has done lots of 
>research about SFRC (Steel Fiber Reinforced Concrete) and has valuable 
>publications for that.
> 
>as far as design, it is really simple. (like a rectangular section of 
>concrete with tensile capacity bellow N.A and compression at top) 
>tensile strength value you can get is a function of the type of fiber 
>you use (length and shape of fiber are really important)
> 
>In general:
>the common percentage of fiber is btwn .5% to 2% and what they are 
>providing in your case is about 1.5% (which is in range) it improves 
>impact ,toughness,tensile strength,cracking behavior and shear 
>resistance of concrete. (advantages) needing more cement in mix (more 
>shrinkage), being usually more expensive (for equivalent design), and 
>its workability are the major disadvantages of that.
>my main concern in your case is adequacy of using only fiber instead of
>#7 @12. based on my rough calc I get half of moment strength. so I
think
>their design should be something like 1.5% fiber in addition to #7
>@24"o/c (or equivalent)
> 
>other concern would be where you have top reinforcing. because if you 
>use SFRC, after you pour concrete most of fibers go to the bot of slab 
>and you will get more tensile strength at bot. So I would probably like

>to keep up to 70% of top reinforcements.
> 
>AM
> 
>
>-----Original Message-----
>From: Meyer, Jonathan [mailto:jmeyer(--nospam--at)webbersmith.com]
>Sent: Thursday, June 17, 2004 3:52 AM
>To: seaint(--nospam--at)seaint.org
>Subject: Steel Fibers Replacing Structural Reinforcing?
>
>
>
>I am currently designing an industrial facility a portion of which is a

>rack supported building. We designed the mat foundation to support this

>building and came up with an 18" thick slab with two layers of #7 bars 
>@12 OCEW. One of the concrete contractors has asked a steel fiber 
>manufacturer to value engineer the reinforcing to determine if they can

>do it with steel fibers instead of the reinforcing specified. There are

>also slab on grade and elevated composite slabs in this facility. 
>That's the background, here is my question - Has anyone replaced 
>structural reinforcing with steel fibers and are there any standards 
>related to such a replacement?
>
>The steel fiber representative called me and told me that they would 
>have to increase the slab thickness to 19" and use 60# of fiber per 
>cubic yard. He invited me to use their software to "verify" the design.

>I guess I am a bit skeptical about using someone else's software that 
>has a vested interest in the outcome of the design to produce a design.

>I told the steel fiber manufacturer that they would have to take full 
>responsibility for the design and produce sealed stamped plans if they 
>wanted to change my designs to steel fiber for the mat slab of the rack

>supported building. As far as the slabs on grade are concerned, I feel 
>that if the client wants to use steel fibers in those areas that would 
>be fine as long as they understand any limitations of the fibers.
>
>Any input would be greatly appreciated. Thanks for you assistance.
>
>Jonathan Meyer
>
>Webber Smith Associates
>
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********