I guess that wasn?t very clear on my part?

Yes, I do design the intermediate anchors for in-plane and out-of-plane
shear in addition to uplift.  

I DON'T usually design the chord anchors for shear because:
-  the uplift tension load is very high (all the uplift in the wall) in
relation to the shear (a very small fraction of the total shear in the
wall).
- the hold-down is usually several inches above the plate so the rod can
deflect without taking much shear load.
- the hole is often right at the end of the bottom plate, so the limiting
shear would be the very low capacity of the plate.

Disclaimer:  This applies to a fairly long wall with lots of intermediate
anchors.  If it's a relatively short wall, or if there are only a few
relatively short intermediate wall segments, then yes, the end anchors will
need to help with the shear.

---
Jason Kilgore
Leigh & O'Kane, LLC
Kansas City, Missouri
________________________________________
From: Eli Grassley [mailto:elig(--nospam--at)psm-engineers.com] 
Sent: Friday, August 27, 2004 2:05 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: Uplift Anchorage at Perforated Shear Wall

I agree with Joe.  The question is?do you design the intermediate anchors
for uplift and shear combined?  That?s how the forces will likely be applied
in a big lateral force event, so regardless of the code I think it would be
best to design for real life load conditions?whatever that means.
 
Eli Grassley
 
-----Original Message-----
From: Joe Grill [mailto:jgrill(--nospam--at)swiaz.com] 
Sent: Friday, August 27, 2004 11:32 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Uplift Anchorage at Perforated Shear Wall
 
It doesn?t appear that is what the IBC ?perforated shear wall? method is
saying.  It is giving equations for both end of wall uplift and uplift to
anchorage between the end walls.
 
-----Original Message-----
From: Jason W. Kilgore [mailto:jkilgore(--nospam--at)leok.com] 
Sent: Friday, August 27, 2004 11:11 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: Uplift Anchorage at Perforated Shear Wall
 
I design the intermediate anchor bolts to handle all in-plane shear and the
end anchors for uplift only.
 
---
Jason Kilgore
Leigh & O'Kane, LLC
Kansas City, Missouri
________________________________________
From: Joe Grill [mailto:jgrill(--nospam--at)swiaz.com] 
Sent: Friday, August 27, 2004 12:03 PM
To: seaint(--nospam--at)seaint.org
Subject: Uplift Anchorage at Perforated Shear Wall
 
I am looking a shear wall using the perforated shear wall provisions in the
2003 IBC.  There are uplift force calculations (2305.3.7.2.4) and in-plane
shear calculations (2305.3.7.2.5) and uplift anchorage between wall ends
(2305.3.7.2.6).  Are the anchor bolts required to be designed for in-plane
shear acting at the same time with the uplift anchorage between wall ends? 
 
 
Thanks,
Joe Grill



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********