Joe,

If you use 16" blocks with shells removed at the center of the wall, you'll
have grouted cells of about 13-1/2" maximum dimension.  Be sure to use a
shrinkage-control admixture such as Pre-Mix Grout Additive, or Sika Grout
Aid in order to minimize the shrinkage of the grout away from the walls of
the CMU units.

Nels Roselund, SE
South San Gabriel, CA
njineer(--nospam--at)att.net


-----Original Message-----
From: Will H [mailto:haynewp(--nospam--at)hotmail.com] 
Sent: Monday, November 08, 2004 4:16 PM
To: seaint(--nospam--at)seaint.org
Subject: RE: 16" thick CMU wall

It sounds like you are designing it as a cantilever wall. I've never relied 
on cmu ties to transfer the shear required for a composite section. I would 
hollow out the inside of the (2)-8" blocks and fill it solid like a 
pilaster.

I would be careful in proceeding with this if the flush face of the blocks 
is going to be at the compression side.



Will Haynes, P.E.




>From: "Michael Bryson" <mbryson(--nospam--at)NYASE.com>
>Reply-To: <seaint(--nospam--at)seaint.org>
>To: <seaint(--nospam--at)seaint.org>
>Subject: RE: 16" thick CMU wall
>Date: Mon, 8 Nov 2004 15:40:30 -0800
>
>I have built 16" CMU walls using two wythes of 8" block wall by:
>
>
>
>1) removing the face shells on one side
>
>2) tying them together with high-lift grout ties
>
>3) provide temporary shoring during grouting
>
>4) add #4 ties between the wythes anchored by horizontal bars at ea.
>face
>
>
>
>Since your wall is only 4'-0" high you can forgo #2 and #3
>
>
>
>You can get 16" block from some manufacturers but they can be of limited
>availability and types.
>
>
>
>-----Original Message-----
>From: Joe Grill [mailto:jgrill(--nospam--at)swiaz.com]
>Sent: Monday, November 08, 2004 2:42 PM
>To: seaint(--nospam--at)seaint.org
>Subject: 16" thick CMU wall
>
>
>
>I have been ask (by the architect, owner, contractor and everyone else
>in town) to change the design of a concrete retaining/basement wall that
>was 12" thick to a CMU wall.  The 16" thickness will reduce to 12" at 4
>ft from the footing and then to 8" at 8 ft from the footing.  At the
>base the CMU will require a 16" thickness.  I am assuming the
>construction will be 2 wythes of 8" CMU.  Is there any special detailing
>required to make the double wythe work?  The wall will be solid grouted
>and will have quite a bit of vertical steel in both faces.  I also have
>horizontal bars at 16" o.c. Is there anything else required?
>
>Thanks,
>
>Joe Grill
>
>
>
>Joseph R. Grill, P.E. (Structural)
>
>Shephard - Wesnitzer, Inc.
>
>Civil Engineering and Surveying
>
>1146 W. Hwy 89A Suite B
>
>Sedona, AZ  86340
>
>PHONE (928) 282-1061
>
>FAX (928) 282-2058
>
>jgrill(--nospam--at)swiaz.com
>
>
>
><http://inet/index.htm>
>
>
>

_________________________________________________________________
Express yourself instantly with MSN Messenger! Download today - it's FREE! 
http://messenger.msn.click-url.com/go/onm00200471ave/direct/01/


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ******** 



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********