Ken,
The difference between the two wind loads is the probability of being exceeded per year (1 in 10 for deflection check(service) and 1 in 30 for strength) and service load is in the range of 80-82% of the other one.

Robert,
The l/720 limit is not a matter of choice here in Vancouver, It is the city code. As for the "Design Guide" of "Western States Clay Products association" Dated January 1995 although it is one of my favorites, the explanation they give as to how they arrived at l/360 (section 2.1.2) has never been good enough for me (working in Vancouver, lots of rain) and it might be just me, but I would choose the more recent publication from US Army Corps of Engineers (TI 809-07 Design of... Masonry Veneer/Steel Stud Walls,30 Nov 1998) to go with.

Reza Dashti P.Eng



From: "Ken Peoples" <kspeoples(--nospam--at)lvta.net>
Reply-To: <seaint(--nospam--at)seaint.org>
To: <seaint(--nospam--at)seaint.org>
Subject: Re: l/600 or l/720 brick veneer light gage back-up
Date: Thu, 9 Dec 2004 07:44:17 -0500

Thanks Reza,

What % range is the reduced wind load that is used for this check?

Best regards,


Ken

Kenneth S. Peoples, P. E.
LVTA
Lehigh Valley Technical Associates, Inc.
1584 Weaversville Road
Northampton, PA 18067

Phone: 610-262-6345
Fax:610-262-8188
Email: kpeoples(--nospam--at)lvta.net

----- Original Message -----
From: "Reza Dashti Asl" <rezadashti(--nospam--at)hotmail.com>
To: <seaint(--nospam--at)seaint.org>
Sent: Wednesday, December 08, 2004 7:48 PM
Subject: Re: l/600 or l/720 brick veneer light gage back-up


> Here in Vancouver,Canada, we design the backup for brick veneer (mostly
> light gauge for me)
> for l/720 deflection limit to avoid cracks and water infilteration. The
wind
> load is not the one used for the strength design (C&C ) but a reduced wind
> load used for the deflection check only, as per our building code. The
l/600
> is the limit for the brick veneer itself and not for the backup (I don't
> remember where I read this one)
> I believe the l/600 limit has been out there for a while. In fact TI
809-07
> (30 Nov 1998) published by US Army Corps of Engineers has a table (page
2-9)
> that specifies l/600 as the deflection limit for the brick veneer over
> sheathed framing.
>
> Reza Dashti, P.Eng
>
>
>
> >From: Jim Wilson <wilsonengineers(--nospam--at)yahoo.com>
> >Reply-To: <seaint(--nospam--at)seaint.org>
> >To: seaint(--nospam--at)seaint.org
> >Subject: Re: l/600 or l/720 brick veneer light gage back-up
> >Date: Wed, 8 Dec 2004 06:33:53 -0800 (PST)
> >
> >Ken,
> >
> >I can't find the article off hand, but I believe that I remember reading
> >something to the effect that the deflection limits were stringent to
> >mitigate the development of micro-cracks in the bed joints to eliminate
> >water infiltration. The NRC Canada comes to mind, but again, that's the > >best guess if I had to Google it again. As far as the appropriate design
> >wind load, I would only add that it seems excessive to design a
> >servicibility criteria like this for the highest possible wind and the
most
> >stringent of deflections.  Perhaps the 0.7 in note f is established for
> >this very reason.  I would like to see the commentary on this note, if
> >there is any.
> >
> >When I worked for one of your occasional light gage panel clients in
> >Bethlehem, we always used L/600 for C&C loads.  That was as much to err
on
> >the side of caution, as it was because we were certain it was the right
> >thing to do. But I must admit, doing so cost the company a lot of money
> >and a lot of arguments because 12ga studs and gage tube steel aren't
cheap,
> >especially when they can't even get a common tech screw to penetrate.
> >
> >If you find anything more, please let me know.  And I also notice that
> >1604.3.4 states that masonry deflection shall not exceed that permitted
by
> >ACI 530.
> >
> >Jim Wilson
> >Stroudsburg, PA
> >
> >Ken Peoples <kspeoples(--nospam--at)lvta.net> wrote:
> >I know that BIA recommends l/600 to l/720 for a brick veneer back-up
> >deflection limitation. They say "for service loads". What I am not sure
> >about is what the design wind pressure for this condition should be.
> >Should this just be based on the same component and cladding design load
> >used for the strength design of the studs or can it be a reduced wind
load.
> >  Table 1604.3 of IBC 2003 indicates that the deflection limit for
exterior
> >walls with brittle finishes should be l/240 and footnote f indicates that > >the load may be 0.7 times the design component and cladding loads. This > >seems to be quite different form BIA's recommendation of l/600. Perhaps
a
> >brick veneer is not considered a brittle finish?
> >
> >Is the l/600 or l/720 specifically required somewhere else in the IBC?
> >
> >Thanks for your help.
> >
> >Best regards,
> >
> >
> >Ken
> >
> >Kenneth S. Peoples, P. E.
> >LVTA
> >Lehigh Valley Technical Associates, Inc.
> >1584 Weaversville Road
> >Northampton, PA 18067
> >
> >Phone: 610-262-6345
> >Fax:610-262-8188
> >Email: kpeoples(--nospam--at)lvta.net
> >
> >
> >
> >
> >---------------------------------
> >Do you Yahoo!?
> > Yahoo! Mail - Find what you need with new enhanced search. Learn more.
>
>
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
*
*   This email was sent to you via Structural Engineers
*   Association of Southern California (SEAOSC) server. To
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
*   send to the list is public domain and may be re-posted
*   without your permission. Make sure you visit our web
*   site at: http://www.seaint.org
******* ****** ****** ****** ******* ****** ****** ********



******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* * This email was sent to you via Structural Engineers * Association of Southern California (SEAOSC) server. To * subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
* Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you * send to the list is public domain and may be re-posted * without your permission. Make sure you visit our web * site at: http://www.seaint.org ******* ****** ****** ****** ******* ****** ****** ********