RE: Minimum Reinforcing for thick slab on ground

[Subject Prev][Subject Next][Thread Prev][Thread Next]

Rich,

You will definitely want to reinforce the top, both for shrinkage/temperature and the fact your machine may cause vibration/impact loads.  If you are in a high seismic area it will also help confine your anchor bolts.

Thomas Hunt, S.E.
ABS Consulting




"Rich Lewis" <sea(--nospam--at)lewisengineering.com>

12/23/2004 09:21 AM

Please respond to
<seaint(--nospam--at)seaint.org>

To
<seaint(--nospam--at)seaint.org>
cc
Subject
RE: Minimum Reinforcing for thick slab on ground





It is a structural slab, in that it is a mat footing for machine equipment.  The top of the mat footing also serves as the slab walking area.  I do have bottom reinforcing running in both of the primary directions.  Top is not required by analysis.  I was wondering if I would get lots of cracks on the top surface from shrinkage and should reinforce for it.

 

 
Rich Lewis
Lewis Engineering

 

-----Original Message-----
From:
THunt(--nospam--at)absconsulting.com [mailto:THunt(--nospam--at)absconsulting.com]
Sent:
Thursday, December 23, 2004 9:51 AM
To:
seaint(--nospam--at)seaint.org
Subject:
Re: Minimum Reinforcing for thick slab on ground

 


Rich,


The first thing to ask is "is this a STRUCTURAL slab?".  If this is a simple slab on grade without significant shears or moments then it is not governed by ACI 318.  If this IS a structural slab, then the temperature steel is only required normal to the flexural reinforcement.  Note also that there is no reason to put it all in the top and for a slab this thick you would probably want to split it top and bottom.


That said, realize a slab this thick will generate a lot of internal heat and a mesh of rebar top and bottom is a very good idea regardless of what the code says.


Thomas Hunt, S.E.

ABS Consulting


"Rich Lewis" <sea(--nospam--at)lewisengineering.com>

12/23/2004 07:20 AM


Please respond to
<seaint(--nospam--at)seaint.org>


To
<seaint(--nospam--at)seaint.org>
cc
 
Subject
Minimum Reinforcing for thick slab on ground

 


   




I am designing a concrete mat, 3 ft. thick, which will serve as the top of slab as well.  My questions is do I need to provide the minimum top steel of 0.0018% of gross area for shrinkage control based on the overall depth?  Is there a reduction for this for extremely thick slabs?

 

 

 
Rich Lewis