Hi,

I am reviewing an existing building with LRFD steel design.  Along the
drag lines of a roof diaphragm are the existing W14x22 beams that
suppose to pass on the collected diaphragm shear to the brace frame at
the end of the building.  I am treating these beams as compression
members just to see if it can take the loads to the brace frame.
(Ignore bending for the moment.)

Fy=36 ksi;
bf/2tf of the W14x22 is 7.46 which meets the flange compactness of 15.9;
h/tw of the W14x22 is 53.3 which is bigger than the compactness of 42.3;
assuming the beam is braced at 15 feet along the weak axis.
Kl/r = 173.1;
Table 3-36 on the manual page 16.1-143 give phi*Fcr = 7.13 ksi.
area = 6.49 sq in
Pall (without reducing for no-compact web) = 7.13*6.49 = 46.3 kips

To account for the reduction on the effectiveness on the web,
I apply the Eq A-B5-12 on pg 16.1-91
(using b=13.7 & t=0.23)
I get "b sub e" = 10.2 inches.   

I than reduce the cross section area form 6.49 - 0.23*(13.7-10.2) =
5.69 sq inches

The new capacity I got is reduced to 40.5 kips.

Question? Am I doing this correctly?

Thanks

Sam

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********