Dennis,

A point of contention...where the state/local jurisdiction has adopted the
IBC (or the BOCA or the SBC since they did the same) as the legal code
(aka "the law"), then ACI 318 (in whatever "flavor" [aka year]) _IS_ the
law.  The IBC code specifically references ACI 318, which technically
makes ACI 318 part of the IBC code.  Now, there will be some
exceptions/modifications included in the IBC that may modify or exempt
some sections of ACI 318.  But, make no mistake...where the IBC is the
"law", this makes ACI 318 the "law"...UNLESS the local jurisdiction/state
elects to "modify" this portion of the IBC (i.e. pass the adoption of the
IBC but the law "deletes" some sections such as the reference to ACI 318).

This is also true for other documents like the NDS, the MSJC (masonry
code), some of the AISC specs (ASD spec, LRFD spec, Seismic spec), and
some other structural standards.

This varies some from what you are used to in the UBC as the UBC does tend
to reprint alot of stuff directly in it.  The 1997 UBC has direct
provisions in the concrete chapter (it so happens that those provisions
are largely identical to ACI 318-95...but then that is because that was
the basis of the UBC's concrete provision...they just "tweaked" things a
little).

Regards,

Scott
Adrian, MI


On Wed, 16 Feb 2005, Dennis S. Wish, PE wrote:

> Ed Tornberg wrote:
>
> > For engineers in “high seismic risk” regions, including the West Coast:
> >
> > Do you specify minimum 3000 psi concrete on all your foundations, and
> > thus trigger special inspection?
> >
> > You are required to do this per ACI 318 21.2.4.1: “Compressive
> > strength f’c of the concrete shall be not less than 3000 psi”
> >
> > - ACI 318 Table R21.2.1 states that Foundations are included in the
> > scope of section 21.2
> >
> > - 2003 IBC confirms and reinforces this, by stating that …Seismic
> > Design Category D, E, or F, …foundations complying with Sections [ACI]
> > 21.2 through 21.10 shall be used to resist [seismic].
> >
> > So I understand that all foundations, including stemwalls, PEMB
> > pedestals, etc. require special inspection. The only exception would
> > be isolated and strip footings.
> >
> > If you state that “design basis is 2500 psi”, you are violating ACI
> > 318 21.2.4.1, correct?
> >
> > Ed Tornberg
> >
> > Tornberg Consulting, LLC
> >
> > 503-551-4165
> >
> Ed,
> In a sense, this is a loaded question. Most of the West Coast still uses
> the 97 UBC and not the 2003 IBC. There is a section in, I believe,
> chapter 19 of the UBC that covers the use of 3,000 psi concrete. This is
> especially true in areas that have specific municipal requirements based
> upon modifications to the state adopted code (which in California is
> based on the 97 UBC). The use of 3,000 psi concrete, beyond its specific
> need for strength in the design, triggers the requirements for special
> deputy inspection and structural observation. This can be required as
> part of the municipal code if in a region where the 97 UBC is not used,
> but the local municipality has deemed it to required.
> The issue you raised is what governs. While I would like to say that
> ACI-318 governs, it is only the method, not the law. What is written in
> the code that you use is law - it was adopted and ratified by the state
> and local municipalities. You can use your judgment to argue the issues
> or to design to the more conservative, but you can not, without a change
> in the code, design to a standard less than that required within in the
> code.
> I think that some years ago when design methods were part of the UBC
> (prior to 1994) this was an easier issue to deal with as discrepancies
> were less common since the section of the code dealing with any material
> contained the general verbiage of the material organizations such as
> ACI, AISC, MIA, AITC etc. I don't particularly think that the split to
> sell separate references was good from the position of a practitioner
> since it left the rhetoric open to confusion and possible error.
> Finally, I don't specify a "design basis" but rather state that the
> minimum strength of concrete to be used must be 2,500 psi or as noted on
> the plans. The contractor is free to use 3,000 psi concrete without
> special inspection and while I have a note that states that all grade
> beams and foundations resisting lateral forces are to be designed per
> section xxxx.xx.x.x of the current code. Furthermore, I specifically
> note the requirements for special inspection and structural observation
> on the plan and on the details. There are times when, for example, I
> need to show a retrofit of an epoxy anchor if omitted or changed during
> construction. If the anchor is for shear only, then deputy inspection
> requirements for epoxy are generally not enforced within most
> municipalities - the local building inspection can check the cleanliness
> of the holes. The same is true when I use rebar dowels to tie a new
> foundation to an existing so as to prevent potential differential
> settlement. Here again, the anchor acts in shear and not tension so just
> sticking a dowel into concrete without epoxy or grouting will still
> achieve the same goal when lateral movement (tension) is not the case.
>
> Hope this helps - just remember that code is law and ACI-318 documents
> are not enforced by law but are assumed to be the basis for the law. If
> the law is worded wrongly and not corrected then theoretically you can
> design to the mistake and be covered. I think this is risky as your
> education and professional intuition can easily be questioned in a court
> of law.
>
> *Dennis S. Wish, PE*
> *California Professional Engineer
> Structural Engineering Consultant
>
> dennis.wish(--nospam--at)verizon.net*
> *
> 760.564.0884 (office - fax)
> *
>
>     */This e-mail is intended to be delivered only to the named
>     addressee(s) and may contain information that is confidential and
>     proprietary. If this information is received by anyone other than
>     the named addressee(s), the recipient(s) should immediately notify
>     the sender by e-mail and promptly delete the transmitted material
>     from your computer and server. In no event shall this material be
>     read, used, stored, or retained by anyone other than the named
>     addressee(s) without the express written consent of the sender or
>     the named addressee(s)./*
>
>
> ******* ****** ******* ******** ******* ******* ******* ***
> *   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
> *
> *   This email was sent to you via Structural Engineers
> *   Association of Southern California (SEAOSC) server. To
> *   subscribe (no fee) or UnSubscribe, please go to:
> *
> *   http://www.seaint.org/sealist1.asp
> *
> *   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you
> *   send to the list is public domain and may be re-posted
> *   without your permission. Make sure you visit our web
> *   site at: http://www.seaint.org
> ******* ****** ****** ****** ******* ****** ****** ********
>

******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********