Rich,

1.  You may want to look at ACI 12.15.3 commentary that says "Such splices need not be staggered, although such staggering is encouraged where the area of reinforcement provide is less than twice that required by the analysis".  From a practical standpoint, you may still need to stagger the splices to avoid congestion.  Some couplers, such as Bar-Lock, can be huge and really do not save you much on space.  Couplers such as the Lenton tapered threaded type are much smaller but require more field work to install.

2.  If your spliced bars are located on the inside (towards the center) then the ties should be the same as normal if I understand your question correctly.

Thomas Hunt, S.E.
ABS Consulting



"Rich Lewis" <seaint02(--nospam--at)lewisengineering.com>

05/12/2005 07:11 AM

Please respond to
<seaint(--nospam--at)seaint.org>

To
<seaint(--nospam--at)seaint.org>
cc
Subject
RE: Large Rebar Detailing





I have another question as I detail some column reinforcing.  
 
1.        If I use Couplers, do they need to be staggered in a column splice?
2.        If I use lap splices, how are cross ties handled?  I have a rectangular shape column with several single cross ties.  Are the ties doubled, one for each bar in the splice?  If so, I would think couplers would be more efficient.
Thanks again.
 
Rich Lewis
 
 
-----Original Message-----
From:
THunt(--nospam--at)absconsulting.com [mailto:THunt(--nospam--at)absconsulting.com]
Sent:
Wednesday, May 11, 2005 11:07 AM
To:
seaint(--nospam--at)seaint.org
Subject:
Re: Large Rebar Detailing

 

Rich,


In addition to the large bend radius problem that you mentioned, here are a couple of more possible issues with large diameter bars:


1.  Lap splices can get VERY long, therefor, make sure they fit in your section (i.e. beam/column).


2.  Related to #1 above, lap splices can cause significant congestion.  In some cases, especially columns, it is best to draw a cross section to scale.  With this in mind, you may need to use mechanical couplers.  Note, however, that mechanical couplers come in many different shapes and sizes and from my experience the cheapest couplers tend to be the largest.


Thomas Hunt, S.E.

ABS Consulting


"Rich Lewis" <seaint02(--nospam--at)lewisengineering.com>

05/11/2005 08:51 AM


Please respond to
<seaint(--nospam--at)seaint.org>


To
<seaint(--nospam--at)seaint.org>
cc
 
Subject
Large Rebar Detailing

 


   





I am detailing some concrete beams and columns with #10 - #14 bars.  I usually don’t detail these large bars.  Are there any words of wisdom someone can share about things to consider using this size bar?  I know one thing I saw in the past is the sweep radius of large bar hooks can cause problems.  Anything else I should be sure to consider?  I do have a beam and column joint to detail.

 
Thanks.

 
 