It is feasible/practical to lower the footing and add a key to resist 
the horizontal thrust?

Rich Lewis wrote:

>In typical PEMB's I use hairpins or tie rods to tie the
>2 ends of the rigid frames.  Since this is 475' long this doesn't seem
>practical.  I see it as 2 options: 1) design the exterior footing for
the
>overturning force.  This will make it a large footing.  2) tie the base
of
>the frame to the first interior column, at one end 150' and the other
end
>120'.  Both have their advantages and disadvantages.
>
>Which method have you typically used for large horizontal thrusts on
long
>span rigid frames?

-----/Original Message-----

What we TYPICALLY do for PEMBs in Texas is have a large grade beam at
the edge, both to transmit wall loads to the soil and to provide
resistance against thrust. There are drilled shaft footings at the
columns, sitting underneath the edge beam. Normally I don't
dowel-connect the pier to the grade beam, but in this case I'd surely
make an exception (and check the interface for direct shear/shear
friction--actually, you might find you don't need the dowels after all).

I haven't done a foundation as large as the one Rich describes, but I
would think this sort of thing would scale reasonably well. Hairpins
plus edge-beam plus drilled shafts with or without dowels across the
interface.


This email and any files transmitted with it are confidential and intended solely for the use of the addressee. If you are not the intended addressee, then you have received this email in error and any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. Please notify us immediately of your unintended receipt by reply and then delete this email and your reply. Tyson Foods, Inc. and its subsidiaries and affiliates will not be held liable to any person resulting from the unintended or unauthorized use of any information contained in this email or as a result of any additions or deletions of information originally contained in this email.


******* ****** ******* ******** ******* ******* ******* ***
*   Read list FAQ at: http://www.seaint.org/list_FAQ.asp
* 
*   This email was sent to you via Structural Engineers 
*   Association of Southern California (SEAOSC) server. To 
*   subscribe (no fee) or UnSubscribe, please go to:
*
*   http://www.seaint.org/sealist1.asp
*
*   Questions to seaint-ad(--nospam--at)seaint.org. Remember, any email you 
*   send to the list is public domain and may be re-posted 
*   without your permission. Make sure you visit our web 
*   site at: http://www.seaint.org 
******* ****** ****** ****** ******* ****** ****** ********