Another issue to consider is thrust bracing where mains and feeder lines do 90 degree turns either vertically and horizontally.  These thrust forces can be 2-5kips in range depending on the hydraulics of the system.  These forces are high in the basements where the pumps are typically located.  There are vertical gravity and thrust hangers to keep the pipe from galloping, but thrust bracing is typically vertical bracing at 45 degrees with 2 pieces.  The direction of flow matters when you lay these bracing systems out.  Hopefully there is some concrete deck available to handle the lateral loads.  Dry systems are especially bad – water hammer; charged systems are a little better.  Also watch out for code requirements in seismic areas.  Fire is a common secondary effect after the shockwaves, so they want the sprinkler systems operational to minimize the damage.  They may require more frequent spacing of vertical and thrust bracing than what calculation show.

 

----------------------------

Boge Boge (1980) Ltd.

Hans E. Boge, P. Eng.

268 Ellen Street

Winnipeg MB, Canada, R3A 1A7

p:(204) 942-7276 ext 223

f:(204) 942-7288

www.boge-boge.com

hanseb(--nospam--at)boge-boge.com

 

-----Original Message-----
From: Bruce Holcomb [mailto:bholcomb(--nospam--at)brpae.com]
Sent: Friday, June 24, 2005 11:48 AM
To: seaint(--nospam--at)seaint.org
Subject: RE: SPRINKLER LOAD

 

When I worked in the metal building industry, we almost always used 3 psf collateral load.  The relatively small piping for typical runs can be covered by 1 psf, but when you get to the larger trunk lines, 3 psf is sometimes not enough.  And for the larger lines, individual attachment points can have very larges applied loads (large as in several hundred pounds), so I typically assume a sprinkler load for design, then back-check the framing once the final sprinkler layout is determined.  3 psf is probably a good starting point, but you need to consider the specific situation.

 

 

BDH

 

-----Original Message-----
From: Jason Atwood [mailto:atwoodjason(--nospam--at)yahoo.com]
Sent: Friday, June 24, 2005 11:28 AM
To: SEAINT(--nospam--at)SEAINT.ORG
Subject: SPRINKLER LOAD

 

HI:

 

WHAT'S A GOOD PSF VALUE TO USE SPRINKLERS? NOTE TYPE V 1 HOUR.

 