The IBC (1805.7.2) provides two formulas in the design criteria to resist lateral forces (flagpole footing design). One formula is for non-constrained and the other for constrained. Also the code allows an increase in the lateral bearing values for flagpoles, or signs not adversely affected by a ½” motion at the ground surface due to short-term loads.

 

I have some questions:

 

1.                   In your opinions what constitutes a constrained condition? The commentary indicates constraint “such as a rigid floor”. Does this mean that there needs to be a physical connection (dowels) between the “rigid element” at the top of the flagpole footing? Would paving (concrete or asphalt) placed right up against the top of the footing constitute a constrained condition?

 

2.                   In your opinions is the ½” motion referred to above as the combination of the pole deflection and the movement of the footing against the soil?

 

3.                   If the footing is constrained, and therefore not actually able to move ½”, can you still take the increase? It seams to me that the intent is that as long as you have a flexible structure that can sustain these deflections the increase is allowable even if those movements are not possible because of the constrained condition at the top of the footing.

 

Thanks for your comments.

 

David  James Puskas, P.E.

Senior Engineer - Structural

 

BSW International, Inc.

BSW International Engineers, P.C.

Thomas F. Keeter, P.E., Inc.

One West Third Street Suite 800

Tulsa, Oklahoma  74103

 

Work Telephone:  918-295-4213

Cellular Telephone:  918-640-2778