I see what you are saying. Unfortunately there are a number of agencies in my area that won’t allow such a justification without surveys of buildings, etc. It is more expensive, sometimes, to justify it than to just bite the bullet.

 

Mark E. Deardorff, Structural Engineer

Burkett & Wong

San Diego, CA


From: S. Gordin [mailto:mailbox(--nospam--at)sgeconsulting.com]
Sent: Monday, January 09, 2006 1:49 PM
To: Seaint@Seaint. Org
Subject: Re: Wind Exposure

 

Mark,

 

Check CBC 1619 and 1619A, Exposure B is definitely allowed, even for OSHPD projects.  I used it many time. 

 

Ed,

 

The subject case could have been Exposure B, except for the fact that Exposure B (and C) definition clearly refers to "terrain" as opposed to "terrain facing large bodies of water" of Exposure D definition.  Therefore, in the subject case, Exposure D is more in line with the apparent intent of the code.

 

Steve Gordin SE
Irvine CA

 

----- Original Message -----

Sent: Monday, January 09, 2006 1:25 PM

Subject: RE: Wind Exposure

 

The State of California B/C does not allow the use of Exposure B under any conditions. You can use C or D however. If you’re not in CA check with your B/D.

 


From: Ed Tornberg [mailto:ed(--nospam--at)tornbergconsulting.com]
Sent: Monday, January 09, 2006 12:33 PM
To: seaint(--nospam--at)seaint.org
Subject: Wind Exposure

 

Let’s say I have a house that’s 600 feet or so from the ocean, West coast.  ASCE 7-02 governs.

 

Between the waterline and the house is a hill, evergreen trees, and other houses.  It’s clearly surface roughness B all around.

 

Question1 :  What is the design wind exposure?

 

Question 2:  would it make any difference if using the 1997 UBC?

 

Thanks,

 

Ed Tornberg