Sam,
 
Could you be more specific about your question?  I ran the axial/moment curve using PCACol v3.0, turning all the phi factors to 1.0, and I got the curve similar to the curve shown on Example 7.8 at Notes on ACI 318-02. 
 
Frank
 
Frank Yang, P.E.
Project Engineer                      BERGER/ABAM Engineers Inc
Voice: 206-431-2374                  33301 9th Ave S, Suite 300
Fax:   206-431-2250                 Federal Way, WA  98003-2600
yang(--nospam--at)abam.com                               http://www.abam.com 

Notice: This message (including any attachments) contains confidential information intended for a specific individual and purpose, and is protected by law.  If you are not the intended recipient, you should delete this message, and any disclosure, copying, or distribution of this message, or the taking of any action based upon it, is prohibited.
 


From: Szuchuan Chang [mailto:szuchuan(--nospam--at)gmail.com]
Sent: Sunday, February 05, 2006 12:21 AM
To: SEAOC; Basile Rabbat; Sam Chang
Subject: Qustion to Robert Mast About PCA Notes Example 7.8 Biaxial Loading

Hi,
 
I don't know how to reach Mr. Robert F. Mast in regarding to questions about PCA Notes Example 7.8 Biaxial Loading.
 
In the example, with Pn = 1846 kips; Mnx = 461.5 & Mny=192.3 ft-kips
 
f'c = 5 ksi and fy=60 ksi.
 
24" square column with 4#11 bars.
 
I ran the loads by pcaColumn version 3.61.  It did not calculate at all!
 
I have to use a 26" square column with 12#11 bars to make it works.
 
PCA Notes is such a good and accurate reference,  which makes me think that I have done something wrong.
 
So if any of you can pass my question to Mr. Mast, I will sully appreciate.
 
Thanks
 